A server and a UPS is not an electrical room nor considered "electrical 
equipment".

"Electrical Rooms" house Transformers, MCCs and Switchgear.  The clue is the 
mention of dry type equipment.   You haven't seen any oil cooled computers have 
you?

So technically this doesn't apply but it depends on what you convince the AHJ 
it means.


If they are adamant about not putting sprinklers in the room, the better 
argument is found in the Fire Code in 903.3.1.1.1 EXEMPT LOCATIONS where you 
could use exemption (2)"Any room or space where sprinklers are considered 
undesirable because of the nature of the contents, when approved by the fire 
code official."  Now the room will require the installation of smoke detectors 
if you omit the sprinklers.  Run that by the AHJ and see if it flies.



Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Thursday, November 19, 2015 2:29 PM
To: [email protected]
Subject: Electrical Equipment room

Opinions please

 

NFPA #13 2013 ed section 8.15.11 Electrical Equipment.

 

Room is used as a server room, only the server and the UPS are in the room, the 
room is 2 hour fire rated.

 

Section 8.15.11.3 Sprinklers shall not be required in electrical equipment room 
where all of the following conditions are met:

 

(1)    Room is dedicated to electrical equipment only        yes

(2)    Only dry-type electrical equipment is used.                Yes

(3)    Electrical equipment is installed in a 2 hour rated enclosure
including protection of penetrations      yes

(4)    No combustibles storage is permitted to be stored in the room.
yes

 

Based on this can the sprinkler heads be eliminated from this room?

 

Would still have to get it by the AHJ.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://secure-web.cisco.com/1zyL-IIfogELwG3Q_nmzTBWVZQNuViT_fQuYwoI05a4DL1fxlpc6ybMm97Qa8tfZSTlzKjSn3Pv38GkPMqgRZRPP8ygUtpi87WN7SJZ25emJTG_VcxyvmhGB5mRoxWdN7rcakv6oPlfa4XkcKIVggNJtZjyGBQBzR9kEqTHWgwywHJIvaY0Zy2DBk07Q7LPSt-8Rczojk3SWFzPjr4mSa-7chtNhTn22s5dxuUjMlhfhitrye1P21e7ID4JpPR2JI-QmVzeiibt4UlRgoW7RFjH-byhNKNrWBQcyQIiPv6_Vx2qS-8CUBnacbTXgV_QW7bJCSfGq-Q5t2pzbI6L5e-7bs-3oxWGuiK84kGsz5IR45s_aQaSNsAntdGchkFrowVQOeWZA2XpecO-zTJLinpBMdnPSjDSLIvp9mPInVJas/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to