Sounds like someone is doing the A/E dance.  Not the first time one has 
attempted to say this means equipment that uses electricity.

If the value of the data or continuity of business warrants it, suggest they do 
a double interlock preaction system.

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Nov 19, 2015, at 11:47 AM, <[email protected]> <[email protected]> 
> wrote:
> 
> A server and a UPS is not an electrical room nor considered "electrical 
> equipment".
> 
> "Electrical Rooms" house Transformers, MCCs and Switchgear.  The clue is the 
> mention of dry type equipment.   You haven't seen any oil cooled computers 
> have you?
> 
> So technically this doesn't apply but it depends on what you convince the AHJ 
> it means.
> 
> 
> If they are adamant about not putting sprinklers in the room, the better 
> argument is found in the Fire Code in 903.3.1.1.1 EXEMPT LOCATIONS where you 
> could use exemption (2)"Any room or space where sprinklers are considered 
> undesirable because of the nature of the contents, when approved by the fire 
> code official."  Now the room will require the installation of smoke 
> detectors if you omit the sprinklers. Run that by the AHJ and see if it flies.
> 
> 
> 
> Craig L. Prahl 