You have several placement options OR provide additional sprinklers.   You have 
to go back to 8.5.5.1 for the text on the additional sprinkler.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Nov 19, 2015, at 12:09 PM, Rocci Cetani 3 <[email protected]> wrote:
> 
> I need some clarification on figure 8.6.5.1.2(b) obstructions against a wall
> which limits the soffit/obstruction to 30" in order to use the equation. So
> for soffits/obstructions against walls over 30"  (and under 4') would you
> use figure 8.6.5.1.2(a)  or would a sprinkler be required underneath it?
> 
> 
> 
> Rocci Cetani III, CET