I don't believe there is a prohibition, but if you take 2 heads off one
outlet,
you had better verify it hydraulically.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic [
https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Fri, Dec 18, 2015 at 2:58 PM, [email protected]
<[email protected]> wrote:
I was always taught when doing an upfit you only replace 1 for 1, meaning if
here was 1 existing head on an arm-over you couldn't say add another "new"
head
and now be feeding 2 heads off that same arm-over, otherwise you'd have to
add a
new arm-over to the branchline for the new head. Now that may have come
from a
spec long long ago but I swore it was also in NFPA, however I don't see it
worded that way in the standard. Any help?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
I've seen wording too. I think it is related to above/below, 1/2 nip
permissible (unless seismic), etc, it's involved, but it's there
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org