Thanks all

I always discuss any restrictions that may be required with the owner and if
the flexibility is required or future growth would be anticipated, then the
entire building will be designed to the higher hazard. Just looking at
options.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  [email protected]





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Wednesday, January 06, 2016 1:31 PM
To: [email protected]
Subject: Re: Mixing ESFR Heads

AS Mark and Duane have already flagged, it is addressed by 13.  Although 13
says 15 ft, check the cut sheet regarding the possible 20 ft.  I seem to
remember there is something on ESFR (a very hazy recollection).

The point I want to make is to ensure you have something in writing showing
the owner is aware that they can not later change the contents of the lower
hazard area by expanding their higher hazard stuff (done without a second
thought).  The flexibility may be worth the cost difference to the owner.
The CYA for you down the road - priceless.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jan 5, 2016, at 3:11 PM, James Crawford <[email protected]>
wrote:
> 
> Looking at a 400,000 sq.ft. building with multiple storage 
> arrangements, on the floor, on single and double row racks. Each about
half the building.
> 
> 
> 
> Can you use K25 ESFR heads for the rack storage (exposed expanded 
> Group A
> plastics) and K17 heads for the storage on the floor (class 4
commodities)?
> 
> 
> 
> Thoughts as I cannot find anything that says you can't.
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  [email protected]
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to