In Seattle even the big parking garages for multi-family, 13 or 13R,  don't
(or at least didn't when I worked for a living) require them on self
closing doors as the doors are considered to be very temporary obstructions
at best. In the what realm though I suppose someone could say, but what if
someone drove a burning car into the garage. People could die.

On Thu, Jan 14, 2016 at 3:59 PM, Roland Huggins <[email protected]>
wrote:

> That because it is not an allowance for 13.  It is in 13R.
>
> 7.3.2.1 Garage doors shall not be considered obstructions and shall be
> permitted to be ignored for placement and calculation of sprinklers.
>
>
>
> Roland
>
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>
>
>
>
>
> > On Jan 14, 2016, at 12:22 PM, Travis Mack, SET <[email protected]>
> wrote:
> >
> > Was having a discussion with a contractor the other day.  Do you guys
> design/install sidewall sprinklers for under garage doors in apartment
> buildings.  I am referring to the garages where it is accessible only by a
> single tenant, not a large parking garage with an apartment complex.  I
> don't find anything in 13 that allows it to be eliminated.  However, we run
> into a lot of these where the sidewall is not installed.  Just curious how
> others approach this.
> >
> > --
> > Travis Mack, SET
> > MFP Design, LLC
> > 2508 E Lodgepole Drive
> > Gilbert, AZ 85298
> > 480-505-9271
> > fax: 866-430-6107
> > email:[email protected]
> >
> > http://www.mfpdesign.com
> > https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> > Send large files to us via: https://www.hightail.com/u/MFPDesign
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to