Line size, not like size. Steve, how do you turn off the stinking spellchecker?

Mark at Aero
602 820-7894

Sent from my iPhone

> On Jan 18, 2016, at 1:59 PM, "[email protected]" <[email protected]> 
> wrote:
> 
> Scott, many if not most like size threaded fittings are now manufactured from 
> ductile iron. It's cheaper than malleable and stronger than cast iron. 
> 
> Mark at Aero
> 602 820-7894
> 
> Sent from my iPhone
> 
>> On Jan 18, 2016, at 1:52 PM, "[email protected]" 
>> <[email protected]> wrote:
>> 
>> B16.4 is for gray iron which I think is the most common form for fire 
>> sprinkler system above ground threaded fittings. 
>> 
>> I'm attempting to determine the applicable standard for ductile iron flanged 
>> fittings AND whether or not such fittings are permissible in the above 
>> ground portion of the fire sprinkler system.  Specifically in the riser 
>> manifold. It could be a flanged ductile iron tee or flanged ductile iron 
>> spool piece, etc. 
>> 
>> I heard that they are being used as I described.  So, I thought I'd look it 
>> up to see if NFPA 13 allowed it.  And, none of the standards listed in the 
>> acceptable materials table address ductile iron.
>> 
>> I'm comfortable with pointing to 1.7 as a "back up" justification.  But, any 
>> more help would be appreciated.
>> 
>>   J. Scott Mitchell, PE
>>      Fire Protection Engineer | 
>>      Projects Engineering
>>      CNS Pantex | 806.477.5883 | 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Matthew J Willis
>> Sent: Monday, January 18, 2016 2:29 PM
>> To: [email protected]
>> Subject: RE: Ductile Iron Fittings
>> 
>> Scott,
>> 
>> Isn't 36.10M for Welded and Seamless pipe?
>> B16.4  is for fittings.
>> 
>> R/
>> Matt
>> 
>> Matthew J. Willis
>> Project Manager
>> Rapid Fire Protection Inc.
>> *NEW ADDRESS*
>> 1530 Samco Road
>> Rapid City, SD 57702
>> Office-605.348.2342
>> Direct Line-605.593.5063
>> Cell-605.391.2733
>> Fax:-605.348.0108
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of [email protected]
>> Sent: Monday, January 18, 2016 7:27 AM
>> To: [email protected]
>> Subject: RE: Ductile Iron Fittings
>> 
>> Thanks for all the responses. 
>> 
>> The reason is because NFPA 13 does not include ductile iron (ASME B36.10M) 
>> in the acceptable materials table. My opinion is that it is functionally 
>> more than adequate. 
>> 
>> Would this be covered by section 1.7 (2016) for alternate arrangements?
>> 
>>   J. Scott Mitchell, PE
>>      Fire Protection Engineer | 
>>      Projects Engineering
>>      CNS Pantex | 806.477.5883 | 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to