Sometimes computers programs don't understand what we humans are trying to say.
Stop the calc's for each system at the junction and do the rest by hand. Then
do a manual graph. I assume the trench system has a higher flow requirement
than the roof system so the available pressure for the roof system will be less
than if you just calc'd the roof system by itself. I have seen different calc
programs deal with pumps in different ways. When that happens I work around the
problem rather than fight the system.
On Thursday, January 28, 2016 7:50 PM, Jerry Van Kolken
<[email protected]> wrote:
Its back at the source a 16" underground at location where the 2 both get
supplied from.
Travis,
That is how I typical today do it just the way this one is set up is
throwing everything off.
Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Ron Fletcher
Sent: Thursday, January 28, 2016 4:02 PM
To: [email protected]
Subject: Re: Balancing Systems
Where is the balance connection point?
Sent from my iPhone
> On Jan 28, 2016, at 6:33 PM, Jerry Van Kolken <[email protected]> wrote:
>
> Any advice on balancing systems from a the same source when one is
> charged with a fire pump and the other is not? I'm working on a AFFF
> hangar system where the new trench system is charged by fire pumps and
> the existing overhead is fed direct from the city supply on the
> opposite side of the building.
>
>
>
> Jerry Van Kolken
>
> Millennium Fire Protection Corp.
>
> 2950 San Luis Rey Rd.
>
> Oceanside, CA 92058
>
> (760) 722-2722 FX 722-2730
>
>
>
> We Have Moved Please update your records with the new address
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org