Bill

Would an hour's time now remove it as an issue in the future? The FD or plan 
reviewing agency might have the original documentation, even if the designing 
firm is gone. A calc plate might close issue. Just note it is recreation, and 
origin of data. 

Is current occupant OH1 or 2, and system obviously to an experienced eye with 
some knowledge of public water system, a fairly beefy system? Comparison: If 
someone uses a 12"x6" steel I-beam for an 8' wide garage door header in a 
one-story ranch with 25 pound snow load, do you need stamped engineering calc's?

Or is occupancy Class A plastics in double row racks to 20', with 8' aisles? 

Best

Bruce


> On Feb 1, 2016, at 13:16, Kevin Eanes <[email protected]> wrote:
> 
> i would just write up the midsing data plate as a definciency on the insp
> report and let the AHJ tell the property owner that he needs to get a calc
> survey.all u can do is get the numbers from the drain test to verify the
> water supply is normal.i doubt anyone will ever push the issue on him but
> as long as its noted on your report your ass is covered
>> On Feb 1, 2016 4:11 PM, "Todd Williams" <[email protected]> wrote:
>> 
>> The survey and Calc is the only way to be sure. I've seen some placards
>> that w
>> ere total crap and it has created problems
>> 
>> Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
>> 860-535-2080 (ofc) 860-608-4559 (cell)
>> Sent using CloudMagic [
>> https://cloudmagic.com/k/d/mailapp?ct=pi&cv=6.0.64&pv=8.2]
>> On Mon, Feb 1, 2016 at 4:03 PM, [email protected]
>> <[email protected]> wrote:
>> A client of mine has posed a question.
>> I understand part of a system inspection is to verify the adequacy of the
>> water
>> supply. Many older buildings are missing the hydraulic placard on the
>> riser, and
>> original plans/calcs are not available.
>> 
>> A full-blown survey and hydraulic calculation is too expensive and the
>> owner
>> will balk at it.
>> 
>> Those of you who are involved in inspections, how do you handle this and
>> what
>> would you recommend?
>> Would a rough 'guestimate' suffice depending on the occupancy?
>> 
>> 
>> Thank you.
>> 
>> 
>> 
>> Bill Menster
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to