NFPA says to see that it conforms with 13 and 25. that would be format, not
data. If it's not there it is a deficiency and needs to be replaced.
(NFPA25/14 Table 5.5.1) Replacement may require a survey and re-calc but
that is outside the scope of 25 and that is explicitly stated in the
document. (NFPA25/14 5.5.3)

On Mon, Feb 1, 2016 at 4:41 PM, Steve Leyton <[email protected]>
wrote:

> We have AHJ'S that will issue,a correction notice for missing placards. If
> it is noted on an inspection as a deficiency, and if you're AHJs want
> copies of inspections to be filed with them, then that would be a
> potential  enforcement benchmark.
>
>
> Steve
>
>
> -------- Original message --------
> From: [email protected]
> Date: 2/1/2016 2:03 PM (GMT-07:00)
> To: sprinklerforum <[email protected]>
> Subject: Hydraulic Placards
>
> A client of mine has posed a question.
> I understand part of a system inspection is to verify the adequacy of the
> water supply. Many older buildings are missing the hydraulic placard on the
> riser, and original plans/calcs are not available.
>
> A full-blown survey and hydraulic calculation is too expensive and the
> owner will balk at it.
>
> Those of you who are involved in inspections, how do you handle this and
> what would you recommend?
> Would a rough 'guestimate' suffice depending on the occupancy?
>
>
> Thank  you.
>
>
>
> Bill Menster
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)