Ahhh, but Ron, if the doors, or openings are or can be left open and the steam 
can 'flow out' if you will, then you have a different scenario and a call to me 
in the future.

I've been involved with sprinklers that operate in MRI rooms causing 
significant damage when hot, moist air accidentally comes out of heating 
equipment through diffusers...

Without knowing all of the conditions and the equipment arrangement and so on 
I'm just sayin'... be safe, put in the sprinklers with the temperature rating 
above the maximum ambient temperature as required by the tables in the Red Book.

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Thursday, February 18, 2016 1:35 PM
To: [email protected]
Subject: Re: Sprinkler Temp Vs. Response type

So let's play Brad a bit. Steam is 212F and a gas so invisible. Steam vapor is 
visible and somewhat below that. It would cool rapidly in contact with air that 
is within a human tolerance range. It should be well below 200 before it 
reaches the ceiling where it will continue to cool as it contacts the sprinkler 
head and its associated mass. No test but I know enough about steam that if you 
can see it it's not steam. And released into the atmosphere it does not get 
hotter, but rather cools.


On Thu, Feb 18, 2016 at 11:15 AM, Michael Hill <[email protected]> wrote:

> Do not have NFPA 13 in front of me, but there is a section that allows 
> you to use SR heads if there are no QR heads in the temperature that you need.
>
> Mike Hill
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]]
> On Behalf Of Jerry Van Kolken
> Sent: Thursday, February 18, 2016 2:12 PM
> To: [email protected]
> Subject: Sprinkler Temp Vs. Response type
>
> I have a situation where there is a parts steam cleaner that will put 
> out
> 250 deg. Steam when opened to remove parts. The sprinklers in the area 
> are quick response type.  I want to put Extra High temp heads (325 
> deg) over the cleaner, but I can only find them in standard response 
> at that temp. Am I being over cautious with that high temp of rating? 
> And would all the heads in the area have to be changed to standard 
> response type?
>
>
>
> Jerry Van Kolken
>
> Millennium Fire Protection Corp.
>
> 2950 San Luis Rey Rd.
>
> Oceanside, CA 92058
>
> (760) 722-2722 FX 722-2730
>
>
>
> We Have Moved Please update your records with the new address
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to