Ahhh, but Ron, if the doors, or openings are or can be left open and the steam can 'flow out' if you will, then you have a different scenario and a call to me in the future.
I've been involved with sprinklers that operate in MRI rooms causing significant damage when hot, moist air accidentally comes out of heating equipment through diffusers... Without knowing all of the conditions and the equipment arrangement and so on I'm just sayin'... be safe, put in the sprinklers with the temperature rating above the maximum ambient temperature as required by the tables in the Red Book. Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of rongreenman . Sent: Thursday, February 18, 2016 1:35 PM To: [email protected] Subject: Re: Sprinkler Temp Vs. Response type So let's play Brad a bit. Steam is 212F and a gas so invisible. Steam vapor is visible and somewhat below that. It would cool rapidly in contact with air that is within a human tolerance range. It should be well below 200 before it reaches the ceiling where it will continue to cool as it contacts the sprinkler head and its associated mass. No test but I know enough about steam that if you can see it it's not steam. And released into the atmosphere it does not get hotter, but rather cools. On Thu, Feb 18, 2016 at 11:15 AM, Michael Hill <[email protected]> wrote: > Do not have NFPA 13 in front of me, but there is a section that allows > you to use SR heads if there are no QR heads in the temperature that you need. > > Mike Hill > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected]] > On Behalf Of Jerry Van Kolken > Sent: Thursday, February 18, 2016 2:12 PM > To: [email protected] > Subject: Sprinkler Temp Vs. Response type > > I have a situation where there is a parts steam cleaner that will put > out > 250 deg. Steam when opened to remove parts. The sprinklers in the area > are quick response type. I want to put Extra High temp heads (325 > deg) over the cleaner, but I can only find them in standard response > at that temp. Am I being over cautious with that high temp of rating? > And would all the heads in the area have to be changed to standard > response type? > > > > Jerry Van Kolken > > Millennium Fire Protection Corp. > > 2950 San Luis Rey Rd. > > Oceanside, CA 92058 > > (760) 722-2722 FX 722-2730 > > > > We Have Moved Please update your records with the new address > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org