I'm with you on this one Ken. Someone is mixing metaphors - thrustblocks
consist of concrete, i.e., UNDG,  so no place to think hanger.
You are the swaybrace guru---anything about concrete for Overhead Pipe?
On Mar 18, 2016 3:29 PM, "Parsley Consulting" <parsleyconsult...@cox.net>
wrote:

> I'm not too terribly clear on how some sort of thrust block is needed,
> unless it were at either end of the line.  This fitting is a "flow though"
> device, with no change of direction.
>
> Is the manufacturer telling us that once the line is put under pressure
> that the fitting can be pushed apart?
>
> Aren't the nearest changes in direction, presuming the entire line is
> CPVC, assembled using solvent welded joints, which by definition are
> restrained joints?
>
> This note on their cut sheet really baffles me.
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, California 92025
> *****Phone 760-745-6181*
> Visit our website <http://www.parsleyconsulting.com/>
>
>
> ***
> On 03/18/2016 11:59 AM, Richard Carr wrote:
>
>> You would have to get creative on the thrust block, unistrut, 90 the end
>> of line to get a hanger to keep the line from pushing apart, if you already
>> had armovers or a line that jogged you should be ok.
>>
>> Richard Carr, SET
>> Branch Manager
>> Cox Fire Protection, Inc
>> 6555 Grace Lane.
>> Jacksonville, Fl. 32205
>> rc...@coxfire.com
>> 904-781-8227
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tony Eggster
>> Sent: Friday, March 18, 2016 2:47 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Re: cpvc sharkbite style fittings?
>>
>> I found their spec sheet - thanks. Those will work for the 1" but
>> unfortunately I need something in 1 1/4" as well. I see they require a
>> thrust block - any idea what that would consist of?
>>
>> On Fri, Mar 18, 2016 at 11:37 AM, Richard Carr <rc...@coxfire.com> wrote:
>>
>> Spears makes it, I have a cut sheet if you need it.
>>>
>>> Richard Carr, SET
>>> Branch Manager
>>> Cox Fire Protection, Inc
>>> 6555 Grace Lane.
>>> Jacksonville, Fl. 32205
>>> rc...@coxfire.com
>>> 904-781-8227
>>>
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum [mailto:
>>> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Richard
>>> Carr
>>> Sent: Friday, March 18, 2016 2:35 PM
>>> To: sprinklerforum@lists.firesprinkler.org
>>> Subject: RE: cpvc sharkbite style fittings?
>>>
>>> FlameGuard GripLoc coupling but only in 3/4 and 1". It is a repair
>>> coupling, no glue needed.
>>>
>>> Richard Carr, SET
>>> Branch Manager
>>> Cox Fire Protection, Inc
>>> 6555 Grace Lane.
>>> Jacksonville, Fl. 32205
>>> rc...@coxfire.com
>>> 904-781-8227
>>>
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum [mailto:
>>> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tony
>>> Eggster
>>> Sent: Friday, March 18, 2016 2:32 PM
>>> To: sprinklerforum@lists.firesprinkler.org
>>> Subject: cpvc sharkbite style fittings?
>>>
>>> Hello all,
>>>
>>> I had someone tell me there are shark-bite style fittings out there
>>> that are listed for fire sprinkler use. I've been searching but have
>>> failed to find any. We have a need for fittings that can be utilized
>>> immediately without having to wait for glue to cure.
>>>
>>> Any direction is appreciated.
>>>
>>> Thanks,
>>> Tony
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@lists.firesprinkler.org
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to