THANKS FOR YOUR RESPONSES. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: March-25-16 1:36 PM To: [email protected] Subject: Re: STANDPIPE
Yes. If you are going to test the standpipe as required then you either need to bring a pump, or you coordinate with the fire department to have a truck brought out for testing. It is in the best interest of the FD to coordinate with these tests. Remember, the end user of the standpipe system is the responding FD. I've seen many jurisdictions where these tests never get done. And, I've seen some where the FD is very active in having these done. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Mar 25, 2016, at 10:29 AM, Troy schieckoff <[email protected]> wrote: > > So we need to ladder a 5 story building to run a test on the system? > Can you direct me to where it says it is just a test connection. I > haven't seen that. Thanks > > Sent from my BlackBerry 10 smartphone on the Rogers network. > Original Message > From: Steve Leyton > Sent: Friday, March 25, 2016 1:28 PM > To: [email protected] > Reply To: [email protected] > Subject: RE: STANDPIPE > > Don't forget that it's intended to be used as a test connection, and any fire > fighting water supply applications are subjective and up to the responding > Fire Department. > > > Steve > > > -------- Original message -------- > From: "rongreenman ." <[email protected]> > Date: 3/25/2016 11:26 AM (GMT-07:00) > To: [email protected] > Subject: Re: STANDPIPE > > On Fri, Mar 25, 2016 at 10:16 AM, Trillium Fire Sprinkler Design Inc. > < [email protected]> wrote: > > . With all the facts about light weight truss construction. > > > > I'm curious if this building is wood framed, or with an unsprinklered > combustible attic space, etc., where there would be a increased > concern, more than usual, about being on the roof. Again, I'm only > curious and not challenging any interpretation. I'm just not seeing > the problem but I haven't been around actual construction for some > time and am somewhat unfamiliar with what's in the field these days. > > -- > Ron Greenman > Instructor > Fire Protection Engineering Technology Bates Technical College > 1101 So. Yakima Ave. > Tacoma, WA 98405 > > [email protected] > > http://www.bates.ctc.edu/fireprotection/ > > 253.680.7346 > 253.576.9700 (cell) > > Member: > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC > > They are happy men whose natures sort with their vocations. -Francis > Bacon, essayist, philosopher, and statesman (1561-1626) > > A problem well stated is a problem half solved. -Charles F. Kettering, > inventor and engineer (1876-1958) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org