Troy,
After a quick read of NFPA 14 [2013], 7.3.2(5), I believe your AHJ
is correct, particularly if there is no access to the roof from the
stair. Grated, that section applies to Class I, however Class III
requires that you meet the locations for I and II.
For reference, the paragraph I'm taking guidance from reads:
7.3.2* Class I Systems. Class I systems shall be provided with 2 1⁄2
in. (65 mm) hose connections in the following locations:
[snip]
(5)*At the highest landing of stairways with stairway access to a
roof, or on roofs with a slope of less than 4 in 12 where stairways
do not access the roof
That looks to me as though the AHJ had it right. If the stair
doesn't access the roof, and the roof is flat, then a hose connection is
required.
hope that helps,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 03/25/2016 9:52 AM, Trillium Fire Sprinkler Design Inc. wrote:
QUESTION: AHJ IS TELLING ME I NEED A HOSE CONNECTION ON THE ROOF.
I HAVE A 5 STORY HOTEL. NO STAIR ACCESS TO ROOF, ONLY A HATCH. FLAT ROOF.
THE SYSTEM IS A WET SYSTEM.
I MOVED THE HOSE CONNECTION FROM THE INTERMEDIATE LANDING BETWEEN THE 4TH
AND 5TH TO THE FINSHED 5TH FLOOR LANDING.SINCE IT STATES TO HAVE THE TOP
MOST CONNECTION AT THE HIGHEST LANDING.
AM I MISSING SOMETHING?
ANY GUIDANCE WOULD BE HELPFUL.
THANKS
TROY S.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org