I see fire pumps and tanks far too often in the center of large structures
 down in the sub-basement.

Sometimes the fire protection engineer in charge is a whiz-bang
Computational Fluid Dynamic simulation artist, but has a disdain for the
sprikler vein of the business.  It can be hard to convince an engineer who
has used a computer to validate smoke dampers for much of their career,
that bricks and mortar work offer better fire protection than MS Windows
activated smoke curtains.  But this is ofen the mentality of the engineer
who is chosen to represent fire protection at the upfront meetings.   Worse
still is a fire protection professional will not even be invited to the
pre-FEED table.  Often the civil or mechanical engineer at pre-FEED locates
the fire pump in close to dead-center of the building,  for what is a good
reason to their thinking:  reduced hydraulic demand to remote areas.

But what they don't consider is in the 1 in 300+ year building fire is:

1. fire department using the fire pump room during live fire operations
2. the water tank is next to these sub basement fire pumps, virtually
assuring wet or leaky conditions years on
3. maintenance and repair suggests someone will have to take the pump out,
and a new pump in, piece by piece.
4. if there is a fire in the basement, it has chance to contaminate the air
consumed by the pump's diesel motor

Many of these buildings are large enough that if they simply put the tank
at grade, they would have enough pressure in the basements from gravity to
operate the first half dozen sprinklers, in the event of fire pump failure.

Fire protection, being a cost item, requires fine diplomatic and
negotiating skills to optimize our systems.  Many jurisdictions have
different tolerances to fire risk than held by North Americans, and to
their credit, these other jurisdictions are much more realistic about
accepting 1 in 300+ year building fire.

Each situation deserves its own evaluation.  But I have yet to find an
occassion  justifying spending 300+k$ on two fire pumps and a tank, only to
install them at the sub-basement of a building.

Thank you all for the excellent discussion and references to OSHA, NFPA 13
and NFPA 20 on this subject.

Scot Deal
Excelsior Fire/Risk Engineering