As a general rule we have always noted if there is missing tile in the room,
(near the edges away from the sprinklers. I know that I have always written
it up as a deficiency if the tile was out within a 5ft area around the
sprinkler. if it’s a small closet or storage room and its missing a tile or
two, then I have written it down as a deficiency as well due to the
potential for the heat loss not allowing for the activation of the
sprinkler.

 As for the missing escutcheons, (this is my opinion) I don’t see why they
wouldn't be a critical deficiency due to the listings on the sprinklers.
The sprinklers are listed with the plate to be installed in the manner for
the plate that it was installed with ( recessed, flush, Concealed, 401).  

But you are definitely correct in the statement that this is a gray area in
NFPA #25.  I guess if we step back and think about the original installation
of the ceilings and sprinklers, when the system was bought off by the fire
marshal, wasn’t it required to have all the tile in at the time of his walk
through? So why wouldn’t the building still be required to have all the
tiles in place on a NFPA 25 inspection.

Michael Goodis     
Estimator, Project Manager
IL#000635   NICET#135586
Key Fire Protection Enterprises LLC
3200 Mike Padgett HWY
Augusta, GA 30906
Office- (706)790-3473
Cell- (706) 220-8822
Fax: (706) 738-2119



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jay Stough
Sent: Thursday, March 31, 2016 8:33 AM
To: Sprinkler Forum
Subject: Missing ceiling tiles

We are having a discussion as to whether missing ceiling tiles are a
deficiency in NFPA 25.  It does not specifically mention it, but it is a
non-critical deficiency if it is missing escutcheons and cover plates on
semi-recessed, recessed and concealed sprinklers.  Wouldn't missing ceiling
tiles create the same problem in a room with a drop ceiling?  I would think
it would really screw up the air flow of heat to the sprinklers if there are
2' X 2' or 2' X 4' holes in the ceilings.

*Jay Stough*
NICET IV LAYOUT
NICET III ITM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to