Valves are open and no paint on the spinklers as far as i know Craig
On Mar 31, 2016 4:23 PM, <[email protected]> wrote:

> So what exactly is the purpose and scope of an inspection?
>
> Craig L. Prahl
> Fire Protection Group Lead/SME
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brad
> Casterline
> Sent: Thursday, March 31, 2016 3:15 PM
> To: [email protected]
> Subject: RE: Missing ceiling tiles
>
> Because that 'impairment' thinking creates endless difficulties for Insp.
> Sprinks.
> Poke your head up through that missing tile and look at the rated wall
> penetrations; does everything still look like the perfect and beautiful and
> approved detail you submitted on your plans?
> My guess is:
> Uhhh, NOPES
> On Mar 31, 2016 1:48 PM, <[email protected]> wrote:
>
> Could you not cite it as deficient or non-compliant if the sprinklers
> exceed the maximum allowable distance below the deck above?
>
> If you had a ceiling 4 ft below the deck with pdt sprinklers in it, we
> know you can't install a sprinklers out in the open 4 ft below the deck
> based on obstructed or unobstructed construction rules.  We also don't
> install sprinklers out in space with pie pans on them anymore either to
> "catch the heat".
>
> Also the ceiling is where the heat collects to set off the room
> sprinklers.  If there is no ceiling or the ceiling is now incomplete, where
> will heat collect, above the ceiling in the unprotected area.  This could
> delay sprinkler operation.
>
> So if the installation was based on a compete ceiling being provided in
> order for sprinklers to operate properly, why wouldn't an incomplete
> ceiling be considered the same as any other impairment?
>
> Craig L. Prahl
> Fire Protection Group Lead/SME
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]]
> On Behalf Of Jay Stough
> Sent: Thursday, March 31, 2016 2:20 PM
> To: Sprinkler Forum <[email protected]>
> Subject: Re: Missing ceiling tiles
>
> I don't see how I can cite the building code, fire code or NFPA 101 if I
> am doing an NFPA 25 inspection.  And as far as allowing openings in the
> ceiling, I am sure there are no sprinklers above the ceiling or that the
> tiles are removed due to the reasons cited in 13.  I guess the best way to
> denote it is as a change in the building per chapter 4 since the code or
> fire official probably did not accept the building with missing tiles or
> they were not missing last year.
>
> *Jay Stough*
> NICET IV LAYOUT
> NICET III ITM
>
> On Thu, Mar 31, 2016 at 2:08 PM, Larrimer, Peter A <
> [email protected]>
> wrote:
>
> > John,
> >
> > I am not sure what your finding is, but I would be careful  when
> > trying to use that for a missing escutcheon for a sprinkler.  That
> > paragraph in NFPA
> > 101 allows a penetration (of a pipe likely) in a smoke barrier that
> > has a fire resistance rating to be sealed by an non-combustible
> > escutcheon plate provided the gap around the pipe isn't greater than
> > 1/2 inch.  It would only apply if the barrier was a smoke barrier with
> > a fire resistance rating and it is a membrane protection (one side of
> > the wall) and it wouldn't actually require an escutcheon plate.  That
> > paragraph in NFPA 101 will likely not be a very helpful reference when
> > trying to require a sprinkler to have an escutcheon.  Hope this helps.
> >
> > Thanks
> >
> > Pete Larrimer
> > VA
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of John
> > Allen, CET, CFPS
> > Sent: Thursday, March 31, 2016 9:40 AM
> > To: [email protected]
> > Subject: [EXTERNAL] RE: Missing ceiling tiles
> >
> > This is the code we use to support our findings:
> >
> > NFPA 101 (2012) 8.5.6.4    Where sprinklers penetrate a single membrane
> of
> > a fire resistance rated assembly in buildings equipped throughout with
> > an approved automatic fire sprinkler system, noncombustible escutcheon
> > plates shall be permitted, provided that the space around each
> > sprinkler penetration does not exceed 1/2 in. (13 mm), measured
> > between the edge of the membrane and the sprinkler.
> >
> > Best Regards,
> >
> > John Allen, CET, CFPS
> > President
> >
> >
> >
> > AFS: Allen Fire & Security
> > Your Safety is Our Success
> > Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180
> >
> >
> >   Please consider the environment before printing this email This
> > email contains proprietary and confidential material for the sole use
> > of the intended recipient and is the sole property of AFS.  Any
> > review, use, distribution or disclosure by others without the
> > permission of the sender is strictly prohibited. If you are not the
> > intended recipient (or authorized to receive for the recipient),
> > please contact the sender by reply email and delete all copies of the
> message.
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of michael G
> > Sent: Thursday, March 31, 2016 9:08 AM
> > To: [email protected]
> > Subject: RE: Missing ceiling tiles
> >
> > As a general rule we have always noted if there is missing tile in the
> > room, (near the edges away from the sprinklers. I know that I have
> > always written it up as a deficiency if the tile was out within a 5ft
> > area around the sprinkler. if it's a small closet or storage room and
> > its missing a tile or two, then I have written it down as a deficiency
> > as well due to the potential for the heat loss not allowing for the
> > activation of the sprinkler.
> >
> >  As for the missing escutcheons, (this is my opinion) I don't see why
> > they wouldn't be a critical deficiency due to the listings on the
> sprinklers.
> > The sprinklers are listed with the plate to be installed in the manner
> > for the plate that it was installed with ( recessed, flush, Concealed,
> 401).
> >
> > But you are definitely correct in the statement that this is a gray
> > area in NFPA #25.  I guess if we step back and think about the
> > original installation of the ceilings and sprinklers, when the system
> > was bought off by the fire marshal, wasn't it required to have all the
> > tile in at the time of his walk through? So why wouldn't the building
> > still be required to have all the tiles in place on a NFPA 25 inspection.
> >
> > Michael Goodis
> > Estimator, Project Manager
> > IL#000635   NICET#135586
> > Key Fire Protection Enterprises LLC
> > 3200 Mike Padgett HWY
> > Augusta, GA 30906
> > Office- (706)790-3473
> > Cell- (706) 220-8822
> > Fax: (706) 738-2119
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]]
> > On Behalf Of Jay Stough
> > Sent: Thursday, March 31, 2016 8:33 AM
> > To: Sprinkler Forum
> > Subject: Missing ceiling tiles
> >
> > We are having a discussion as to whether missing ceiling tiles are a
> > deficiency in NFPA 25.  It does not specifically mention it, but it is
> > a non-critical deficiency if it is missing escutcheons and cover
> > plates on semi-recessed, recessed and concealed sprinklers.  Wouldn't
> > missing ceiling tiles create the same problem in a room with a drop
> > ceiling?  I would think it would really screw up the air flow of heat
> > to the sprinklers if there are 2' X 2' or 2' X 4' holes in the ceilings.
> >
> > *Jay Stough*
> > NICET IV LAYOUT
> > NICET III ITM
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to