The key is to make sure that you have the correct Module #14 for the property 
that you are doing. Many different revisions and the latest isn't always the 
one that the developer is contracted to. Make them issue you the module #14 
that you are bound to for your specific project. We also do a 4 head 
calc....fyi...

Rod at Rapid

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Friday, April 01, 2016 10:38 AM
To: [email protected]
Subject: Re: Marriott Module 14 and dwelling units

Thanks everyone, I appreciate the info.  I was leaning towards using it, but 
just wanted to make sure there wasn't going to be a problem at the end, you 
know?

Have a great weekend!


Benjamin Young

On Fri, Apr 1, 2016 at 12:35 PM, Travis Mack, SET <[email protected]>
wrote:

> Read the residential design section of NFPA 13 for the provisions for 
> the
> 4 sprinkler calc.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
>
> On 4/1/2016 9:32 AM, Mel Herrell wrote:
>
>> What is meant by four head calc.?
>>
>> Mel
>>
>>
>>
>> Best regards
>>
>> Melvin
>>
>>
>> On Fri, Apr 1, 2016 at 10:02 AM, Travis Mack <[email protected]> wrote:
>>
>> I do several of their properties per year. I always do the 4 head 
>> calc
>>> without issue.
>>>
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> "Follow" us on Facebook:
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to MFP Design via:
>>> https://www.hightail.com/u/MFPDesign
>>>
>>> Sent from my iPhone
>>>
>>> On Apr 1, 2016, at 8:01 AM, Ben Young <[email protected]> wrote:
>>>>
>>>> Has anyone had any experience doing a 4-head NFPA 13 dwelling unit 
>>>> calculation in Marriott properties?  I have the latest Module 14, 
>>>> and it doesn't mention anything about it at all.  Nothing 
>>>> explicitly states its allowed or not allowed.
>>>>
>>>> Thanks,
>>>>
>>>> Benjamin Young
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
>>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to