Sprinkler connections are permitted to standpipes however, any such connection must be furnished with both a check and control valve (6.3.5.1). There is not a hazard group restriction or a wet/dry restriction on the type(s) of systems that can be connected if I recall correctly.
The foregoing is my opinion only and is not intended to represent the NFPA 14 Technical Committee, nor serve as an interpretation of the standard. Steve Leyton ________________________________________ From: Sprinklerforum <[email protected]> on behalf of Alexandre Lupien <[email protected]> Sent: Thursday, April 28, 2016 7:30 PM To: [email protected] Subject: combination riser NFPA 13-2013 art.8.17.5.2.1 mentions: In buildings of light or ordinary hazard occupancy, 21⁄2 in. hose valves for fire department use shall be permitted to be attached to wet pipe sprinkler system risers. 1- Is it acceptable to attach a pipe to a class I standpipe riser in a stairwell to feed an outside sprinkler room. The room would include three wet pipe sprinkler systems with alarm check valves and individual control valves. 2- Is it acceptable to have an auxiliary dry pipe sprinkler valve fed by a combination standpipe/sprinkler riser? 3- Is it acceptable to have a storage occupancy protected by sprinklers from a combination standpipe/sprinkler riser? Thanks Alex Lupien _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org