Sprinkler connections are permitted to standpipes however, any such connection 
must be furnished with both a check and control valve (6.3.5.1).   There is not 
 a hazard group restriction or a wet/dry restriction on the type(s) of systems 
that can be connected if I recall correctly.

The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve Leyton

________________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Alexandre Lupien <[email protected]>
Sent: Thursday, April 28, 2016 7:30 PM
To: [email protected]
Subject: combination riser

NFPA 13-2013 art.8.17.5.2.1 mentions: In buildings of light or ordinary hazard 
occupancy, 21⁄2 in. hose valves for fire department use shall be permitted to 
be attached to wet pipe sprinkler system risers.



1-      Is it acceptable to attach a pipe to a class I standpipe riser in a 
stairwell to feed an outside sprinkler room. The room would include three wet 
pipe sprinkler systems with alarm check valves and individual control valves.

2-      Is it acceptable to have an auxiliary dry pipe sprinkler valve fed by a 
combination standpipe/sprinkler riser?

3-      Is it acceptable to have a storage occupancy protected by sprinklers 
from a combination standpipe/sprinkler riser?



Thanks

Alex Lupien



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to