With the publishing of NFPA Standard 13D for one and two family dwellings, and 
NFPA 13R for low rise residential occupancies, both of which exempt bathroom of 
55 sq. ft. or less, there may have been some confusion. For example, a four 
story apartment building would be equipped as defined in NFPA 13R while a four 
story  hotel would be equipped as required by NFPA 13. The reference to hotels 
and motels in NFPA 13 makes it clear and consistent that the omission of 
sprinklers is applicable to the residential use buildings, even if they are 
more than four stories, and not applicable to a commercial occupancy such as a 
department store with bathrooms.
Just thinking out load. 

Ed Foster, Fire Marshal
Not a member of any technical committee


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steele, Andrew
Sent: Tuesday, May 03, 2016 1:43 PM
To: '[email protected]' 
<[email protected]>
Subject: RE: NFPA 13 2013 ed bathroom sprinklers

I would suggest that the thinking for hotel/motel uses only was that temporary 
stay occupants wouldn't have opportunity to install significant amounts of 
combustible materials into a bathroom.  However home/apartment occupants do.  
As a Fire Official, I've seen some pretty significant fires originating within, 
and consuming,  bathrooms  (think candles, lots of furnishings, including 
wicker towel shelving units, etc.). 

Andrew Steele




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to