For those of you who get to the 2013 NFPA 13 via the 2015 IBC/IFC references in 
Section 903... please note how ICC codes reacted by adding Section 903.3.1.1.2:

903.3.1.1.2 Bathrooms. In Group R occupancies,
other than Group R-4 occupancies, sprinklers shall
not be required in bathrooms that do not exceed 55
square feet (5 m2) in area and are located within
individual dwelling units or sleeping units, provided
that walls and ceilings, including the walls and ceilings
behind a shower enclosure or tub, are of noncombustible
or limited-combustible materials with a
15-minute thermal barrier rating.

Respectfully,

David Blackwell 

David Blackwell, P.E.
Chief Engineer
(803)896-9833

Office of State Fire Marshal
141 Monticello Trail | Columbia, SC 29203
http://scfiremarshal.llronline.com/
(803)896-9800

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Tuesday, May 03, 2016 6:16 PM
To: [email protected]
Subject: Re: NFPA 13 2013 ed bathroom sprinklers

*** SCDLLR NOTICE *** This email is from an external email address. Please use 
caution when deciding whether to open any attachments or when clicking links 
inside the email.

Don wins.

The TC intentionally restricted the allowance then said hmmm we seems to be 
standing in a pile of manure and despite it being embarrassing reversed their 
decision the next cycle.  I applaud not allowing the ego (aka avoidance of 
embarrassing actions) to dictate their course of action.

So for those working with the 2013 edition, discuss the equivalency rule based 
on the 2016 edition for current jobs.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On May 3, 2016, at 11:22 AM, Don Casey <[email protected]> wrote:
>
> A rethink.....i think
>
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Greg McGahan
> Sent: 2016/05/03 2:22 PM
> To: [email protected]
> Subject: NFPA 13 2013 ed bathroom sprinklers
>
> Does anyone know why the 2010 Ed and 2016 Ed of 13 allow the omission 
> of sprinklers in bathrooms ​in​  "Dwelling Units" but ​ the ​
> 2013
> ​Ed ​
> limits the omission to bathrooms in hotel/motels?
>
>
>
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to