Here is the verbiage from 2009 IBC (just because that is what I had in my 
notes)...

Section 410 - Stages and Platforms

410.7 Standpipes. Standpipe systems shall be provided in accordance with 
Section 905.

905.3.4 Stages. Stages greater than 1,000 square feet in area shall be equipped 
with a Class III wet standpipe system with 1 1/2-inch and 2 1/2-inch hose 
connections on each side of the stage.

Exception: Where the building or area is equipped throughout with an automatic 
sprinkler system, a 1 1/2-inch hose connection shall be installed in accordance 
with NFPA 13 or in accordance with NFPA 14 for Class II or III standpipes.

905.3.4.1 Hose and cabinet. The 1 1/2-inch hose connections shall be equipped 
with sufficient lengths of 1 1/2-inch hose to provide fire protection for the 
stage area. Hose connections shall be equipped with an approved adjustable fog 
nozzle and be mounted in a cabinet or on a rack.

If you choose to install a 1 1/2" hose connection in accordance with NFPA 13, 
go to 8.17.5 (2013 ed.).


Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Friday, May 6, 2016 4:04 PM
To: [email protected]
Subject: RE: Hose Valves for Stage

Have you read the building code for your state?   In CA, we amend the IBC so I 
can't be sure of where you'll find it, but for us the script is in 905.3.4.  
It's the designer's option and there are scenarios for both.

SL

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Friday, May 06, 2016 1:57 PM
To: [email protected]
Subject: RE: Hose Valves for Stage

Steve-
Are you saying the 1-1/2" is correct or the 2-1/2" with the reducer? If the 
2-1/2" what's the point of the reducer?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Friday, May 06, 2016 4:39 PM
To: [email protected]
Subject: RE: Hose Valves for Stage

Yes because that's what the building code provides for if the building is fully 
sprinklered.  It can be arranged either as a standpipe system or as hose valves 
supplied by the sprinkler system.

Steve L.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Friday, May 06, 2016 12:56 PM
To: [email protected]
Subject: Hose Valves for Stage

What's the consensus for the required hose valve size on a high school stage? 
I've done several schools and the AHJ has always allowed 1-1/2" valves since 
they would only be used in a "clean-up" type capacity. A/E now wants me to 
change them to 2-1/2" valves with a 1-1/2" threaded reducer. Make sense to 
anybody?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to