Here is the verbiage from 2009 IBC (just because that is what I had in my notes)...
Section 410 - Stages and Platforms 410.7 Standpipes. Standpipe systems shall be provided in accordance with Section 905. 905.3.4 Stages. Stages greater than 1,000 square feet in area shall be equipped with a Class III wet standpipe system with 1 1/2-inch and 2 1/2-inch hose connections on each side of the stage. Exception: Where the building or area is equipped throughout with an automatic sprinkler system, a 1 1/2-inch hose connection shall be installed in accordance with NFPA 13 or in accordance with NFPA 14 for Class II or III standpipes. 905.3.4.1 Hose and cabinet. The 1 1/2-inch hose connections shall be equipped with sufficient lengths of 1 1/2-inch hose to provide fire protection for the stage area. Hose connections shall be equipped with an approved adjustable fog nozzle and be mounted in a cabinet or on a rack. If you choose to install a 1 1/2" hose connection in accordance with NFPA 13, go to 8.17.5 (2013 ed.). Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Friday, May 6, 2016 4:04 PM To: [email protected] Subject: RE: Hose Valves for Stage Have you read the building code for your state? In CA, we amend the IBC so I can't be sure of where you'll find it, but for us the script is in 905.3.4. It's the designer's option and there are scenarios for both. SL -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Friday, May 06, 2016 1:57 PM To: [email protected] Subject: RE: Hose Valves for Stage Steve- Are you saying the 1-1/2" is correct or the 2-1/2" with the reducer? If the 2-1/2" what's the point of the reducer? Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Friday, May 06, 2016 4:39 PM To: [email protected] Subject: RE: Hose Valves for Stage Yes because that's what the building code provides for if the building is fully sprinklered. It can be arranged either as a standpipe system or as hose valves supplied by the sprinkler system. Steve L. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Friday, May 06, 2016 12:56 PM To: [email protected] Subject: Hose Valves for Stage What's the consensus for the required hose valve size on a high school stage? I've done several schools and the AHJ has always allowed 1-1/2" valves since they would only be used in a "clean-up" type capacity. A/E now wants me to change them to 2-1/2" valves with a 1-1/2" threaded reducer. Make sense to anybody? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org