> *Subject:* Re: NFPA 14 / Remote FDC / Manual Stand-pipes
>
>
>
> Leyton will probably say I'm an idiot but you cannot have any valving
> between the FDC and the house connections on the standpipe. Attach after
> the back flow, or pump, or what have you, but make sure it's after the last
> valve on the municipal line.
>
>
>
> On Mon, Jun 6, 2016 at 8:32 AM, John Irwin <
> jir...@criticalsystemsolutions.com> wrote:
>
> When using a remote FDC on the underground line or the backflow device,
> how do we get around NFPA 14 2010 6.4.1 “*Except for the valve required
> by 6.3.2, shutoff valves shall not be installed between the FDC and the
> system*”?
>
>
>
> I have done many yard FDCs on four story hotels over the years and have
> never had this question come up. NFPA 13 has an exception to allow for a
> remote FDC or an FDC tied in to a header, but 14 doesn’t seem to have this
> same exception. I should note we have combination standpipes. Standpipes
> will be manual wet.
>
>
>
>
>
> *John Irwin*
>
> Sprinkler Construction Manager
>
>
>
>
> *Critical System Solutions, LLC *2830 Scherer Drive, Suite 300
> St. Petersburg, FL  33716
> Office: 727.209.5122
>
> Fax:      727.209.5126
>
> Cell:     813.618.2781
>
> Email:  jir...@criticalsystemsolutions.com
>
>
>
> [image: CSS Logo]
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
>
> --
>
> Ron Greenman
>
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> rongreen...@gmail.com
>
> 253.576.9700
>
>
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com

253.576.9700

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to