Jerry,
from the 2013 edition:
11.5.2 For a manual standpipe, a fire department pumper orportable
pump of a capacity to provide required flow and pressureshall be
used to verify the system design by pumping intothe fire department
connection.
Steve Leyton pointed that out to me a few years back.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 07/14/2016 1:50 PM, Jerry Van Kolken wrote:
We have an AHJ that is asking us the contractor to provide a fire
truck for testing the 100psi at the top of a manual standpipe. We
would like to ask if it is the responsibility of the contractor to
provide a pumper for the standpipe or what experience anyone has had
in the past dealing with this type of situation in the past. And if
there would be any code reference for this test?
Jerry Van Kolken
/_Millennium Fire Protection Corp._/
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org