Jerry,
from the 2013 edition:

   11.5.2 For a manual standpipe, a fire department pumper orportable
   pump of a capacity to provide required flow and pressureshall be
   used to verify the system design by pumping intothe fire department
   connection.

Steve Leyton pointed that out to me a few years back.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 07/14/2016 1:50 PM, Jerry Van Kolken wrote:

We have an AHJ that is asking us the contractor to provide a fire truck for testing the 100psi at the top of a manual standpipe. We would like to ask if it is the responsibility of the contractor to provide a pumper for the standpipe or what experience anyone has had in the past dealing with this type of situation in the past. And if there would be any code reference for this test?