This happened once to me and it was the backflow opening and closing checks, 
does the pressure change on the gauge?  

We took out the checks and it worked beautifully, then got both 3# checks and 
it worked.  Silver bullet.

If not, then I would agree on trapped air expanding and contracting.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Thursday, July 21, 2016 1:56 PM
To: [email protected]
Subject: Re: Resi Riser - Character set not allowed

 

I'm seeing a consensus here that the problem has to do with the cushioning 
effect of air and that eliminating air inside the piping is a good idea. 

 

On Thu, Jul 21, 2016 at 10:45 AM, Mark Phillips <[email protected] 
<mailto:[email protected]> > wrote:

Air Vent up High

 

From: Sprinklerforum [mailto:[email protected] 
<mailto:[email protected]> ] On Behalf Of 
rongreenman .
Sent: Thursday, July 21, 2016 1:15 PM
To: [email protected] 
<mailto:[email protected]> 
Subject: Resi Riser - Character set not allowed

 

Anyone experienced this before? 

 

The original CSC version of the Tyco rest riser in four inch. 

 

http://tyco-fire.com/index_link.php?link=TFP962 
<http://tyco-fire.com/index_link.php?link=TFP962&_ga=1.123267982.464632162.1469119864>
 &_ga=1.123267982.464632162.1469119864

 

Flow throw the IT port and you can watch the lever in the flow switch move and 
then, before alarming, move back to the static condition and essentially reset 
the diaphragm timing. Watch it long enough and listen to the flow and you can 
identify the flows changing the pitch suggesting turbulence. After a bit you 
can identify and  the tones and know when the paddle will move (indicated by 
the lever) and when it will retreat back to what appears a low flow situation. 

 

The flow switch works fine when flowing the main drain but not throw the test 
orifice, although the technician asking me this question says it worked last 
year. All I can figure is there are lots of corners in solved and the flow 
keeps going from a laminar to turbulent pattern and the paddle resets during 
the turbulent period. It seems to me the flow switch and the test outlet are 
too close together but this is the only one of these I've ever seen this 
particular problem occur on and it is a listed device that's been around for a 
long time in both CSC and Tyco livery. 

 

I suggested the technician try the flow test again at a different time of day 
and see what happens. That won't correct the problem but if it works it 
suggests that the problem was due to a temporary condition (maybe repeating) of 
the water supply. 

 

Any other ideas?

 

-- 

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected] <mailto:[email protected]> 

253.576.9700 <tel:253.576.9700> 

 

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958)


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





 

-- 

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected] <mailto:[email protected]> 

253.576.9700

 

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958)