Thanks to everyone who responded. Turnout was overwhelming. That worked to
my advantage as I had a dual purpose. First was your opinions, but secondly
OI wanted to show a young padawan the value of asking questions when
stumped or encountering something new. When I asked if he'd read everything
you guys had written and what he thought he responded, "Awesome!" Thanks.

On Fri, Jul 22, 2016 at 5:05 AM, Dewayne Martinez <
[email protected]> wrote:

> Tom,
>
> We had the same problem with a Silver Bullet too.
>
> Had to switch out the checks.
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Tom Duross
> *Sent:* Thursday, July 21, 2016 1:09 PM
> *To:* [email protected]
> *Subject:* RE: Resi Riser - Character set not allowed
>
>
>
> This happened once to me and it was the backflow opening and closing
> checks, does the pressure change on the gauge?
>
> We took out the checks and it worked beautifully, then got both 3# checks
> and it worked.  Silver bullet.
>
> If not, then I would agree on trapped air expanding and contracting.
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *rongreenman
> .
> *Sent:* Thursday, July 21, 2016 1:56 PM
> *To:* [email protected]
> *Subject:* Re: Resi Riser - Character set not allowed
>
>
>
> I'm seeing a consensus here that the problem has to do with the cushioning
> effect of air and that eliminating air inside the piping is a good idea.
>
>
>
> On Thu, Jul 21, 2016 at 10:45 AM, Mark Phillips <[email protected]>
> wrote:
>
> Air Vent up High
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *rongreenman
> .
> *Sent:* Thursday, July 21, 2016 1:15 PM
> *To:* [email protected]
> *Subject:* Resi Riser - Character set not allowed
>
>
>
> Anyone experienced this before?
>
>
>
> The original CSC version of the Tyco rest riser in four inch.
>
>
>
>
> http://tyco-fire.com/index_link.php?link=TFP962&_ga=1.123267982.464632162.1469119864
>
>
>
> Flow throw the IT port and you can watch the lever in the flow switch move
> and then, before alarming, move back to the static condition and
> essentially reset the diaphragm timing. Watch it long enough and listen to
> the flow and you can identify the flows changing the pitch suggesting
> turbulence. After a bit you can identify and  the tones and know when the
> paddle will move (indicated by the lever) and when it will retreat back to
> what appears a low flow situation.
>
>
>
> The flow switch works fine when flowing the main drain but not throw the
> test orifice, although the technician asking me this question says it
> worked last year. All I can figure is there are lots of corners in solved
> and the flow keeps going from a laminar to turbulent pattern and the paddle
> resets during the turbulent period. It seems to me the flow switch and the
> test outlet are too close together but this is the only one of these I've
> ever seen this particular problem occur on and it is a listed device that's
> been around for a long time in both CSC and Tyco livery.
>
>
>
> I suggested the technician try the flow test again at a different time of
> day and see what happens. That won't correct the problem but if it works it
> suggests that the problem was due to a temporary condition (maybe
> repeating) of the water supply.
>
>
>
> Any other ideas?
>
>
>
> --
>
> Ron Greenman
>
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> [email protected]
>
> 253.576.9700
>
>
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
>
> --
>
> Ron Greenman
>
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> [email protected]
>
> 253.576.9700
>
>
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)