Heat/smoke detectors and we use 200F standard response sprinklers.  The
detectors shut down the elevator before the sprinkler head goes off.  I
have sent in this request to the elevator inspector also but they are not
very quick to respond.



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Forest Wilson
*Sent:* Friday, July 22, 2016 7:59 AM
*To:* [email protected]
*Subject:* Re: Elevator piping



In addition to this forum, I would also consult the Elevator Code. Maybe
call your state elevator code inspector.
How will you do the stunt trip if you arrange the piping this way?



On Jul 22, 2016 7:47 AM, "Dewayne Martinez" <[email protected]>
wrote:

Can I run pipe into the elevator shaft, supply the head in the pit and then
use the same pipe to supply and terminate in the elevator  machine room?  I
have done the opposite order and supplied the machine room first then the
head in the pit but that was only one penetration through the elevator
shaft.  This job I am on is out of sequence for the build so I can’t supply
it the normal way but they still want the elevator in service.

Thanks,

Dewayne