Be careful on the Balcony.  If you are using an IBC based building code it 
supersedes that and adds a statement requiring sprinklers on residential 
balconies with type V construction when using 13D 
See 903.3.2.1.1 NFPA 13R Sprinkler systems  
903.3.1.2.1 Balconies and decks. 

David M. Canham
Fire Systems Solutions
15 Sayles Avenue
Lincoln, RI 02865
Office 401-725-1089
Fax 401-725-1583
Cell 508-277-FIRE (3473)

> On Aug 24, 2016, at 2:05 PM, Easter, Timothy <[email protected]> wrote:
> 
> I know you are using 2007 edition, but the 2013 edition’s introduction states 
> “Further clarification
> was also added stating that sprinklers are not required on balconies or 
> balcony closets.”
>  
> Feel free to contact me with any questions.
> Regards,
> Timothy Easter, PE
> Fire Protection Engineer, Fire Protection
> D +1-757-306-6712
> [email protected]
> 
> AECOM
> 1500 Wells Fargo Center,
> 440 Monticello Avenue,
> Norfolk, VA 23510, USA
> 
> aecom.com
> 
> Built to deliver a better world
> 
> LinkedIn  Twitter  Facebook  Instagram
> 
> <image001.png>
>  
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Mike Stossel
> Sent: Wednesday, August 24, 2016 1:53 PM
> To: [email protected]
> Subject: Sprinklers in mechanical closets on balconies
>  
> The current code for this area is NFPA 13R, 2007.
>  
> I am in a discussion with an engineer regarding the need for sprinklers in a 
> mechanical closet located on a balcony.  My stance is that they are needed, 
> and the engineer is in disagreement stating that he has done this same design 
> all over the country, and has never protected the closet.  The closet 
> contains mechanical equipment that is not fuel fired.  A supply and return 
> duct penetrate the wall into the dwelling unit and are fire stopped; however, 
> they do not have fire dampers.  It was always my understanding that for the 
> opening to be considered protected fire dampers are needed.  When the duct 
> work did not contain them I have always sprinkled the closet.  Am I incorrect 
> and have I been protecting these closets unnecessarily?
>  
> Thanks for the help.
>  
> <image004.jpg>
>  
>  
>    Mike Stossel SET
>    NICET Level IV
>    Automatic Sprinkler System Layout
>    1070 38th Street
>    Brooklyn N.Y. 11219
>    Office: 718-633-3036 ext 114
>    Fax:      718-633-4593
>    [email protected] 
>   www.safetyfiresprinkler.com 
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to