I agree as well. Some of these flex hose assemblies can have 50+' of equivalent length. I would want it calculated to make sure it still works.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 8/30/2016 7:39 AM, Steve Leyton wrote:

To underscore John’s point, these fittings impose with a SUBSTANTIAL pressure loss. As 3^rd party, we would ask for calculations to prove the performance of the revised configuration.

SL

*From:*Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Michael Hill
*Sent:* Tuesday, August 30, 2016 6:11 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: Flexheads in small renovation

I agree with Richard, it needs to be evaluated. It is known that flex piping is generally more demanding than their hard piped counterparts. If the base building design did not include flex piping, I would look at it as a change to base building design and perform a quick calculation to see how it looks. I assume they didn’t use excessively long flex pipe with more bends or lops than were needed.

Mike Hill

*From:*Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Todd Williams
*Sent:* Tuesday, August 30, 2016 8:39 AM
*To:* sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org>
*Subject:* RE: Flexheads in small renovation

This is a single story building. Multiple looped 4" and 3" cross mains with branches to wings. (Think nursing home with interior court yards). No fire pump. 100 psi static with a flat curve (2 year old test, DeltaE = 0). Area in question not most hydraulically remote but toward that end of the building. Branch lines are fed from the loop, not a DE branch main. LH occupancy.

I am not worried about this not being adequate, more a consensus of what needs to be done and what is correct.

Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-608-4559 (cell)

Sent using CloudMagic <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>

On Tue, Aug 30, 2016 at 8:22 AM, Richard Carr <rc...@coxfire.com <mailto:rc...@coxfire.com>> wrote:

    I can’t disagree with John (Hi John) but we need more info to make
    the call,

    In remote area?

    Fire pump?

    What is safety margin on existing?

    What is friction loss on the flex?

    Just because you add 4 flex piping to an existing system does not
    require it to be calculated. But does need to be evaluated.

    Richard Carr, SET

    Branch Manager

    Cox Fire Protection, Inc

    6555 Grace Lane.

    Jacksonville, Fl. 32205

    rc...@coxfire.com <mailto:rc...@coxfire.com>

    904-781-8227

    *From:*Sprinklerforum
    [mailto:sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf
    Of *John Irwin
    *Sent:* Tuesday, August 30, 2016 7:14 AM
    *To:* sprinklerforum@lists.firesprinkler.org
    <mailto:sprinklerforum@lists.firesprinkler.org>
    *Subject:* RE: Flexheads in small renovation

    I disagree with Richard. (Hi Richard!)

    Relocating these sprinklers with flex heads may very well change
    the location of the most hydraulically remote area to the place
    you are working. Flex-heads come with a substantial pressure loss.
    Even if doing calculations wasn’t required, I would want to do
    them for myself for peace of mind. My belief has always been that
    you can’t tax the system without verifying that it still works.

    *John Irwin*

    Manger – Fire Sprinkler Division

    *Critical System Solutions, LLC
    *Cell: 813.618.2781

    Email: jir...@criticalsystemsolutions.com
    <mailto:jir...@criticalsystemsolutions.com>

    *From:*Sprinklerforum
    [mailto:sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf
    Of *Richard Carr
    *Sent:* Tuesday, August 30, 2016 7:08 AM
    *To:* sprinklerforum@lists.firesprinkler.org
    <mailto:sprinklerforum@lists.firesprinkler.org>
    *Subject:* RE: Flexheads in small renovation

    Are the relocates in the remote area? if not I would not calc.
    also , some flex brands are better that others as far as friction
    loss.

    Richard Carr, SET

    Branch Manager

    Cox Fire Protection, Inc

    6555 Grace Lane.

    Jacksonville, Fl. 32205

    rc...@coxfire.com <mailto:rc...@coxfire.com>

    904-781-8227

    *From:*Sprinklerforum
    [mailto:sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf
    Of *Todd Williams
    *Sent:* Tuesday, August 30, 2016 6:30 AM
    *To:* sprinklerforum@lists.firesprinkler.org
    <mailto:sprinklerforum@lists.firesprinkler.org>
    *Subject:* Flexheads in small renovation

    I have a client that did a 4 sprinkler relocate job in an office
    and used Flexheads (no sprinklers added). If the sprinklers were
    connected with hard pipe, I would probably not do hydraulic
    calculations. Given that we have FHs, should I be doing a full 900
    or 1500 sqft calculation?

    Todd G Williams, PE

    Fire Protection Design/Consulting

    Stonington, CT

    860-535-2080 (ofc)

    860-608-4559 (cell)

    Sent using CloudMagic
    <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>



_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to