Vince,
While figure a.9.1.1(a) shows it through the joist, the caution seems to be
what they are driving at. It can be run above joists if the insulation can
be secured to maintain protection.



*Glen Bue**low*

*Glen W. Buelow, Inc.*
*Fire Protection Design and ConsultingCleveland 330.220.7201 <330.220.7201>
*●* Akron 330.665.4439 <330.665.4439>*

On Tue, Aug 30, 2016 at 1:38 PM, Vince Sabolik <[email protected]> wrote:

>  Good afternoon, forum.
>
> We're looking at a redo of a 13D that had CPVC in the unsprinklered
> trussed attic space under
> the insulation but above the bottom chord.
>
> OK or not?
>
> I've read the manufacture's pamphlets - and well, depending on which eye
> you want to close...
>
> Anybody know for sure?
>
>
> thanks, smart people -- Vince
>
>