Thanks for the responses.  However I spoke to the Fire Sprinkler Guru and yes 
at this time you must follow the obstruction rule for the ESFR sprinkler.  
Hopefully in the future there will be some adjustment in the standard for the 
light & ordinary use, but not as of yet.  So for now, if the tenant puts in a 
25” duct or 2’ x 4’ light fixture, you either drop an ESFR sprinkler underneath 
or remove the ESFR system and install conventional.  I think almost everyone 
agrees that the ESFR system would control the light or ordinary hazard, but the 
book is the book at this time.

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, August 31, 2016 1:47 PM
To: [email protected]
Subject: RE: ESFR - Ordinary Hazard

I don’t think Gregg is worried about the first 36” below sprinkler for spray 
pattern development.  I think he is probably more concerned with the rules 
stating obstructions X wide need to be located Y distance horizontally from 
sprinkler.  When a new tenant comes in, they like to run their new lights and 
ducts all over the place without a care in the world and a box checker comes in 
and says an ESFR sprinkler is obstructed even though the new light/duct is more 
than 10ft below the sprinkler and is only 30” wide (not a problem for CMDA 
sprinklers).

My personal opinion is if you follow the obstruction rules so the pattern can 
fully develop (aka first 36”).  Then the other obstruction rules for ESFR 
shouldn’t apply in a light/ordinary hazard occupancy.  With the exception that 
if the obstruction is over 4ft wide then sprinklers need to be under them.  
However, I do not believe this stance is explicitly stated in NFPA 13.

But can any sane person really argue that a sprinkler that will dump more than 
100gpm can’t “control” an OH fire where the CMDA sprinklers that max out at 
23gpm can.  I’ve heard the naysayers argument, “ESFR is 12 sprinklers over 
1200sq.ft which is a fast response sprinkler over a smaller area to quickly 
extinguish a fire”.  Okay then, my argument is I am installing large K-factor 
sprinklers 25K@7psi.  I will calculate 5 per line (50ft > 46.5ft) over 3 lines 
(1500 sq.ft.).  I will still flow less water than the original ESFR system was 
designed for and have a remote area equal to what is now required by LH/OH CMDA 
sprinkler design.  Plus I am also putting at least 4x the amount of water on a 
fire to “control” it.  That 30” duct doesn’t seem to be much of an issue to me 
anymore.

Like I said before, my opinion only.  I am only on the committee for “NFPA ? - 
Wondering Why This Wasn’t Implemented When The Allowance For The Other 
Associated Issue Was”.

Thanks,
Sean VG





From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Wednesday, August 31, 2016 11:17 AM
To: 321; 
[email protected]<mailto:[email protected]>
Subject: RE: ESFR - Ordinary Hazard

Especially since Chapter 8 and rules are divided by the Sprinkler Type, not 
hazard.

R/
Matt

From: Sprinklerforum 
[mailto:[email protected]]<mailto:[mailto:[email protected]]>
 On Behalf Of 321
Sent: Wednesday, August 31, 2016 12:14 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: ESFR - Ordinary Hazard

I would think that the obstruction rules of NFPA 13 Ch 8 would apply to the 
ESFR (i.e. 36" clear below deflector) regardless of the hazard. ESFR's were 
developed and listed by U.L. with additional room below the head to allow for 
the "Discharge Umbrella" to develop.

Just my opinion...

John W. Farabee,

On Wednesday, August 31, 2016 1:37 PM, Gregg Fontes 
<[email protected]<mailto:[email protected]>> wrote:

2016 NFPA 13 – 8.4.6.6 Occupancy and Hazard.  (Handbook)  In an existing 
warehouse building being converted to a non-storage use, the existing ESFR 
sprinklers can remain in place provided the new use is either light or ordinary 
hazard.  My questions is if it is ordinary hazard occupancy, do the ESFR 
obstruction rule apply or due the obstruction rules for standard systems apply 
(i.e. conventional)?  As an example, would 30” x 48” lights be allowed to hang 
below the ESFR sprinkler and not be considered an obstruction?   Same with new 
duct work greater than 24”? Etc.
Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to