Good call-- easier when it converts back to storage in a couple years :)
On Aug 31, 2016 4:18 PM, "Gregg Fontes" <[email protected]> wrote:

> Thanks for the responses.  However I spoke to the Fire Sprinkler Guru and
> yes at this time you must follow the obstruction rule for the ESFR
> sprinkler.  Hopefully in the future there will be some adjustment in the
> standard for the light & ordinary use, but not as of yet.  So for now, if
> the tenant puts in a 25” duct or 2’ x 4’ light fixture, you either drop an
> ESFR sprinkler underneath or remove the ESFR system and install
> conventional.  I think almost everyone agrees that the ESFR system would
> control the light or ordinary hazard, but the book is the book at this
> time.
>
>
>
> Thanks,
>
> Gregg Fontes
>
> Cen-Cal Fire Systems, Inc.
>
> 209-334-9119
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *[email protected]
> *Sent:* Wednesday, August 31, 2016 1:47 PM
> *To:* [email protected]
> *Subject:* RE: ESFR - Ordinary Hazard
>
>
>
> I don’t think Gregg is worried about the first 36” below sprinkler for
> spray pattern development.  I think he is probably more concerned with the
> rules stating obstructions X wide need to be located Y distance
> horizontally from sprinkler.  When a new tenant comes in, they like to run
> their new lights and ducts all over the place without a care in the world
> and a box checker comes in and says an ESFR sprinkler is obstructed even
> though the new light/duct is more than 10ft below the sprinkler and is only
> 30” wide (not a problem for CMDA sprinklers).
>
>
>
> My personal opinion is if you follow the obstruction rules so the pattern
> can fully develop (aka first 36”).  Then the other obstruction rules for
> ESFR shouldn’t apply in a light/ordinary hazard occupancy.  With the
> exception that if the obstruction is over 4ft wide then sprinklers need to
> be under them.  However, I do not believe this stance is explicitly stated
> in NFPA 13.
>
>
>
> But can any sane person really argue that a sprinkler that will dump more
> than 100gpm can’t “control” an OH fire where the CMDA sprinklers that max
> out at 23gpm can.  I’ve heard the naysayers argument, “ESFR is 12
> sprinklers over 1200sq.ft which is a fast response sprinkler over a smaller
> area to quickly extinguish a fire”.  Okay then, my argument is I am
> installing large K-factor sprinklers 25K@7psi.  I will calculate 5 per
> line (50ft > 46.5ft) over 3 lines (1500 sq.ft.).  I will still flow less
> water than the original ESFR system was designed for and have a remote area
> equal to what is now required by LH/OH CMDA sprinkler design.  Plus I am
> also putting at least 4x the amount of water on a fire to “control” it.
> That 30” duct doesn’t seem to be much of an issue to me anymore.
>
>
>
> Like I said before, my opinion only.  I am only on the committee for “NFPA
> ? - Wondering Why This Wasn’t Implemented When The Allowance For The Other
> Associated Issue Was”.
>
>
>
> Thanks,
>
> Sean VG
>
>
>
>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Matthew
> J Willis
> *Sent:* Wednesday, August 31, 2016 11:17 AM
> *To:* 321; [email protected]
> *Subject:* RE: ESFR - Ordinary Hazard
>
>
>
> Especially since Chapter 8 and rules are divided by the Sprinkler Type,
> not hazard.
>
>
>
> R/
>
> Matt
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *321
> *Sent:* Wednesday, August 31, 2016 12:14 PM
> *To:* [email protected]
> *Subject:* Re: ESFR - Ordinary Hazard
>
>
>
> I would think that the obstruction rules of NFPA 13 Ch 8 would apply to
> the ESFR (i.e. 36" clear below deflector) regardless of the hazard. ESFR's
> were developed and listed by U.L. with additional room below the head to
> allow for the "Discharge Umbrella" to develop.
>
>
>
> Just my opinion...
>
>
>
> John W. Farabee,
>
>
>
> On Wednesday, August 31, 2016 1:37 PM, Gregg Fontes <[email protected]>
> wrote:
>
>
>
> 2016 NFPA 13 – 8.4.6.6 Occupancy and Hazard.  (Handbook)  In an existing
> warehouse building being converted to a non-storage use, the existing ESFR
> sprinklers can remain in place provided the new use is either light or
> ordinary hazard.  My questions is if it is ordinary hazard occupancy, do
> the ESFR obstruction rule apply or due the obstruction rules for standard
> systems apply (i.e. conventional)?  As an example, would 30” x 48” lights
> be allowed to hang below the ESFR sprinkler and not be considered an
> obstruction?   Same with new duct work greater than 24”? Etc.
>
> Thanks,
>
> Gregg Fontes
>
> Cen-Cal Fire Systems, Inc.
>
> 209-334-9119
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to