> On Sep 13, 2016, at 08:29, Fox, Duane T. (FireMarshal) 
> <[email protected]> wrote:
> 
> I have reviewed a couple of these in my jurisdiction.  There are a couple of 
> issues that you will need to resolve before you can make a determination of 
> system requirements.  First is the distilling process itself coming off the 
> still is a highly flammable liquid, that will then be cut to a less flammable 
> liquid.  The first part is a Class IB FCL which requires at least a 0.45 
> gmm/sqft density.  Once cut, it will then depend on how much it is cut, 
> alcohol content ranging from 60% to about 25% is a Class IC FCL, 25% to about 
> 8% is a Class II, and the rest is Class IIIA.  Next will be the storage 
> process.  NFPA 30 will give guidance, once they give you the storage amount 
> and configuration.  All my projects distilled a small amount at a restaurant 
> so storage was not an issue.  I will be getting on of the larger storage 
> buildings soon at the Dogfish Head Brewery in DE.
>  
> Good Luck.
>  
>  
> Duane T. Fox, Jr., CFPS, CFI, CFPE
> Asst Chief, Technical Services
> DE State Fire Marshal’s Office
> 302-856-5298
>  
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Tim Stone
> Sent: Tuesday, September 13, 2016 11:16 AM
> To: [email protected]
> Subject: Distilleries
>  
> I need some assistance with a Distillery project. I am working with an 
> Architect on this project and the Owner is anxious and is requesting cost 
> estimates for the Fire Protection Sprinkler system.
> I have indicated that the owner needs to hire an insurance to underwrite and 
> specify the sprinkler system requirements.  
>  
> The project is roughly 33,000 SF., to include Distillery, Indoor storage of 
> Spirits in wood barrels, Processing Facility, Mercantile space, Event and 
> Office spaces.
> The Good news is that there is a great public water supply available on site. 
> Fire Pump and onsite water storage should not be required.
>  
> At this time the Owner would like to get a Square foot price (budget 
> estimate) on the sprinkler system. Can any one assist?
>  
> If necessary please contact me directly off the forum.
>  
> Thank you in advance.
>  
> Regards,
> G. Tim Stone
>  
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
>  
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                            [email protected]
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to