We have a multi-tenant warehouse building, 43,000 ft², it will be divided
into 3 tenant spaces of about 14,300 ft² each with loading bays in the rear
of the warehouse and allowance for 3,000 ft² of office at the front of each
tenant space. The warehouse space will be designed for high pile storage
utilizing ESFR sprinkler heads. As the building will be shell coverage the
AHJ is saying we require 2 sprinkler zones as we are over 40,000 ft²

 

We have allowed for 1 sprinkler zone for the building on the assumption the
rear of the warehouse is used for loading and unloading with no high
storage, there will be future office space up to 3,000 ft², this would allow
a system up to 52,000 ft², and we would be 43,000 ft²

 

Any comments or direction that will allow our assumption

 

 

Thank you

 

 