Like the Mech Tee problem I sited last week, in this case the additional 
friction losses must be taken into account so you could need another 30psi or 
more at the head.

Regards,

Russell Gregory

Christchurch, New Zealand.

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Thursday, 10 November 2016 11:23 AM
To: [email protected]
Subject: RE: ESFR retrofit

 

I agree that there would be a lot of friction there. 

 

The fitting would be ¾” weld-o-let to  3/4” brass nipple (male-male) to 3/4 by 
1 reducer (female-female) to sprinkler head.

 

But any code prohibitions?

 

Matt Grisé PE*, LEED AP, NICET II  
Vice President – New Construction 
Alliance Fire Protection 

130 w 9th Ave.
North Kansas City, MO 64116


*Licensed in KS & MO 

 

913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Wednesday, November 09, 2016 3:44 PM
To: [email protected]
Subject: RE: ESFR retrofit

 

Measure the ID of the brass nipple.

The ID is near 1”.

Can you get a 1x3/4 male reducer. Think about velocity and turbulence at  ~ 125 
gpm

 

Art

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Wednesday, November 09, 2016 4:15 PM
To: [email protected]
Subject: ESFR retrofit

 

I am looking at a warehouse space that needs to upgrade from K14 ESFR to K22. 
Typically this would involve plugging the ¾” outlets and cutting in new 1” 
mechanical T’s.

 

I had someone ask why we could not use a ¾” brass nipple and a ¾” to 1” reducer 
to  up-size the outlet to hold a 1” head. I feel like this is not allowed, but 
I could not find specifically where. It would not really be an extension 
fitting. ¾” brass is allowed. Each change of size is done with a single piece 
reducer. The ¾” tee and nipple would be included in the calculations…

 

Any help on where the code addresses this setup?

 

Thanks!

 

Matt Grisé PE*, LEED AP, NICET II  
Vice President – New Construction 
Alliance Fire Protection 

130 w 9th Ave.
North Kansas City, MO 64116


*Licensed in KS & MO 

 

913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 

 

 

 

  _____  


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 Image removed by sender. Avast logo

This email has been checked for viruses by Avast antivirus software. 
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
  

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to