The code path is:

A:  this is not an extension (which is limited to LH & OH) so change paths

B:  8.15.20.5 supersedes the 1 inch limit (23.4.1.2) and allows a nipple up to 
4 inches.  It also states to include it in the calc.

As you already stated, the huge pressure drop typically kills this for high 
flow heads.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Nov 9, 2016, at 1:14 PM, Matt Grise <[email protected]> wrote:
> 
> I am looking at a warehouse space that needs to upgrade from K14 ESFR to K22. 
> Typically this would involve plugging the ¾” outlets and cutting in new 1” 
> mechanical T’s.
>  
> I had someone ask why we could not use a ¾” brass nipple and a ¾” to 1” 
> reducer to  up-size the outlet to hold a 1” head. I feel like this is not 
> allowed, but I could not find specifically where. It would not really be an 
> extension fitting. ¾” brass is allowed. Each change of size is done with a 
> single piece reducer. The ¾” tee and nipple would be included in the 
> calculations…
>  
> Any help on where the code addresses this setup?
>  
> Thanks!
>  
> Matt Grisé PE*, LEED AP, NICET II  
> Vice President – New Construction 
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
> 
> *Licensed in KS & MO
>  
> 913.888.0647 ph 
> 913.888.0618 f 
> 913.526.7443 cell 
> www. AFPsprink.com <http://afpsprink.com/>
>  
>  
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to