There are a lot more rules for obstructions than just the 48" rule.  Look at 
Chapter 8 of NFPA 13.

There are a lot of designers I've dealt with that don't even know about the 
rules in chapter 8 (which is pretty sad and a poor testament with regard to 
training) and they think if they are 48" or less they're fine.  Sorry but that 
is not entirely true.




Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of very Cool
Sent: Wednesday, January 11, 2017 7:14 PM
To: [email protected]
Subject: Light as an obstruction [EXTERNAL]

I have a project where ceiling lights is hung from the ceiling. The light is 
48" so technically we do not have to sprinkler under it (code requires 
sprinkler under obstruction more than 4 feet wide), but I am wondering what to 
be done if this was 49 inches. This light is located more than 4 feet from 
ceiling slab and putting sprinkler under it is not an option architecturally. 
Wondering if anyone came across this scenario.
P.s. Light is a solid round shape with 48" diameter

Ramez