The second paragraph of 8.6.5.2.1  tells us that if you have a solid continuous 
obstruction you go back to 8.6.5.1.  (so that nixes taking the structural get 
out of jail card).  It 2010 that’s all the standard said so if you had a duct  
and its top was 5 inches below the deflector, it still sent you back treating 
its like a beam.  In 2013, it was added that it applies when the TOP of the  
obstructions is level with or above the deflector.

  
Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Jan 14, 2017, at 4:39 PM, Travis Mack <[email protected]> wrote:
> 
> ll get it fixed. I just wanted to confirm that I couldn't use the "structural 
> members only" exclusion for this. It seems the general consensus is that it 
> needs arm overs or sprigs. No exceptions.  