> On Jan 17, 2017, at 3:16 PM, Steve Leyton <st...@protectiondesign.com> wrote:
> 
> Okay, great and wonderful but you what that does is flatten the curve and 
> potentially makes higher flow rate residual pressures plot HIGHER than they 
> would otherwise be.   Soooooooo … as a designer-of-record charged with (among 
> myriad other things) anticipating worst case scenario, methinks it makes 
> sense to keep as much tilt in that flow data curve as possible.
>  
> Steve L.
> (My opinion only, based on numerous cases served as an expert witness and 
> somebody who buys a lot of liability insurance every year.)
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Dewayne Martinez
> Sent: Tuesday, January 17, 2017 1:13 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Static pressure after backflow preventer
>  
> Ames got back to me and said “Yes there is a pressure loss at static flow. It 
> will depend on which type backflow youre looking at. A RPZ will usually show 
> a 10-15 PSI drop. A double check is usually 8-10.”
>  
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Brad Casterline
> Sent: Thursday, January 12, 2017 12:51 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Static pressure after backflow preventer
>  
> Matt,
>  
> I think your example of sliding friction is excellent. Pressure is force 
> divided by area, and force is mass times acceleration.
> With sliding friction the force required to give a mass an acceleration is 
> greater than the force required to keep it going a constant velocity.
> With fluid friction viscosity comes into play and is actually related to 
> sliding friction in that the constant force required to slide a steel plate 
> across the surface of a fluid, imparting a certain constant velocity to the 
> plate is a measure of the viscosity of the fluid.
>  
> But the question is regarding friction loss when the flow is 0 GPM, and at 0 
> GPM the velocity of the water = 0.
> Near the end of what I pasted you see:
> mgh=1/2mv^2.
> This is the Conservation of Energy formula for going from Potential Energy 
> (static), to Kinetic Energy (residual).
> In a closed system no mass is gained or lost (it is the same on both sides so 
> it cancels out), so,
> h=v^2/2g, and,
> v=SQRT(2gh).
> But if the velocity is 0 on both sides the only way to get a different force 
> measurements is with different h measurements (elevations).
>  
> I know you and others know all this, so please excuse my didactic tone.
>  
> Brad  
>  
> <image001.jpg>
> <image002.jpg>
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Matt Grise
> Sent: Thursday, January 12, 2017 6:33 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Static pressure after backflow preventer
>  
> Of course – if you are super close to a pressure limit – the BFP might also 
> lock in some unusually high pressure spike that occurs in the system. Then 
> the sprinkler system could sit around locked at a pressure that is greater 
> than even the typical measured static.
>  
> Matt
>  
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Matt Grise
> Sent: Thursday, January 12, 2017 6:30 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Static pressure after backflow preventer
>  
> Just to think out loud – I don’t have a perfect understanding of how very low 
> flow works through backflows… but:
>  
> It seems like the system static that is locked in is usually pretty close to 
> the flow test static. I wonder if the noticeable pressure loss to initially 
> open the BFP, that goes down once flow starts, if that pressure drop might 
> approach zero as the flow goes from positive back to zero.
>  
> That is – the pressure drop seen at a flow that is just barely over zero 
> depends on whether you are approaching that flow from zero, or from [more 
> than zero].
>  
> For example: if you slide a block across a table – the force it takes to move 
> the block at a very low speed will depend a lot on whether you start from a 
> standstill, or a faster speed. (that illustrates a different principle, but 
> shows how the approach could change)
>  
> Thoughts?
>  
> Matt 
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Roland Huggins
> Sent: Wednesday, January 11, 2017 6:07 PM
> To: SprinklerFORUM
> Subject: Re: Static pressure after backflow preventer
>  
> I'm flying by the seat of my pants (with no lights) but until I prove to 
> myself otherwise (or am beat into submission by the technical committee), I 
> don’t see why we should beat ourselves up and default to what ever seems to 
> be the most conservative.  Our supply curve is a straight line relationship 
> from static to some lower residual pressure.  We now incorporate a device 
> that has a crazy high initial pressure loss that then drops back into a more 
> normal curve.  In looking at SYSTEM DEMAND are we well served by ignoring the 
> actual available pressure that was otherwise lost due to accounting for a 
> wiggle at the front end.
>  
>  For now, I’ll stick with my mantra:  Lead the way, Mr. Custer. I’m right 
> behind you.
>  
>  
> Roland Huggins, PE - Senior VP Engineering
> American Fire Sprinkler Assn.    
> Dallas, TX
> http://www.firesprinkler.org
>  
> Fire Sprinklers Saves Lives
>  
>  
>  
>  
> On Jan 11, 2017, at 12:27 PM, Dewayne Martinez 
> <dmarti...@total-mechanical.com> wrote:
>  
> I have used the static without the backflow loss in the past but I noticed 
> with the SprinkCad software I am running it uses the mfg curves and it was 
> showing less static than I had figured.  If I take into account the BFP loss 
> I can eliminate 6 pressure reducing hose valves…..Looks like I will err on 
> the side of caution and design them in.
> Thanks,
> Dewayne
>  
>  
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org