Hello Ken, thanks for responding.

So California adopts the IFC with California amendments and then calls it the 
CFC, correct?



-----Original Message-----
From: Parsley Consulting <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Mon, Jan 23, 2017 10:27 am
Subject: Re: PIV Supervion, lock or tamper switch?


    Owen,
        
            The California Fire Code is very specific, and it would seem        
unambiguous for the conditions you describe.  
          
903.4          Sprinkler system supervision and alarms. All valves controlling 
the water          supply for automatic sprinkler systems, pumps, tanks, water  
        levels and temperatures, critical air pressures and water-flow switches 
         on all sprinkler systems shall be electrically supervised by a listed  
        fire alarm control unit. 
              
Exceptions:
        1. Automatic            sprinkler systems protecting one- and 
two-family dwellings.
            Doesn't apply to the buildings you've              described
            
          2.            Limited area systems serving fewer than 20 sprinklers.
        Doesn't apply to the buildings you've              described
              
            3. Automatic sprinkler systems installed in            accordance 
with NFPA 13R where a common supply main is used to supply both            
domestic water and the automatic sprinkler system, and a            separate 
shutoff valve for the automatic sprinkler system is            not provided.
        Depending                  on the underground supply, might or might 
not apply
          
            4. Jockey pump control valves that are sealed or locked in the open 
position.
            Doesn't apply to the PIV
            
          5.            Control valves to commercial kitchen hoods, paint spray 
booths or dip            tanks that are sealed or locked in the open position.
          Doesn't apply to the PIV
            
        6. Valves            controlling the fuel supply to fire pump engines 
that are sealed            or locked in the open position.
          Doesn't apply to the PIV
            
        7. Trim valves to            pressure switches in dry, preaction and 
deluge sprinkler            systems that are sealed or locked in the open 
position.
          Doesn't apply to the PIV
          
    
        It does appear,        based entirely on the information you've 
provided, that        electrical supervision is required for the PIV.
        
            And, not to split hairs or to be pedantic, California is not        
under the regulations in the 2013 IFC.  California, as it does        with 
almost everything, has made it's own modifications to that        document and 
has issued the 2013 California Fire Code, which has        as of January 1 been 
replaced with the 2016 edition of the CFC.             
         
            Chapter 80 of that document contains a list of the        
applicable editions of various standards and codes, including        the NFPA 
documents.  Further, that chapter of the CFC contains        language on 
changes to the NFPA documents.  As an example - in        California, the 
reduction of the remote area size for use of        quick response sprinklers 
in an area with a ceiling height of        20' or less is not allowed in 
ordinary hazard occupancies, even        though NFPA 13 does allow that 
reduction.  
        
             I've had to deal with some terribly angry contractors who        
were unaware of those provisions.  They've said some pretty        creative and 
hostile things when I've pointed them out,        including some I'm sure 
aren't true, as I have a photo of my        parents' wedding, and it was 14 
years before I was born!
        
        sincerely,
          
Ken Wagoner,          SET
          Parsley Consulting
          350 West 9th Avenue, Suite 206
            Escondido, California 92025
                        Phone 760-745-6181
                        Visit our              website          
    

      On 01/23/2017 9:25 AM, Owen Evans wrote:
    
    
        
          
            As most of you              know, I work exclusively with 13D 
systems. I do on              occasion get questions on the big boy systems, 13 
and 13R.               The property in question is a boutique hotel, two        
      buildings. One building is a two story, fifty room hotel              and 
the other building is two story, restaurant on the              first floor and 
banquet facility on second floor with a              roof deck. Each building 
has a FDC and a PIV. I am in              California which is under the 2013 
IFC.              

              
                          
I recently had the question asked "does the PIV                require 
electrical supervision?"  NFPA states a lock is                adequate, the 
2013 IFC states electrical supervision is                required, with 
exceptions. I get different answers form                different people. I'm 
thinking it's the more restrictive                 2013 IFC. Which is it?
              

              
              
Thank you,
              
Owen Evans
                      
        
            
      
      
      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

    
    
  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to