Owen,
    for at least the last fifteen years that has been the case.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 01/23/2017 10:40 AM, Owen Evans wrote:
Hello Ken, thanks for responding.

So California adopts the IFC with California amendments and then calls it the CFC, correct?


-----Original Message-----
From: Parsley Consulting <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Mon, Jan 23, 2017 10:27 am
Subject: Re: PIV Supervion, lock or tamper switch?

Owen,

The California Fire Code is very specific, and it would seem unambiguous for the conditions you describe.

    903.4 Sprinkler system supervision and alarms. All valves
    controlling the water supply for automatic sprinkler systems,
    pumps, tanks, water levels and temperatures, critical air
    pressures and water-flow switches on all sprinkler systems shall
    be electrically supervised by a listed fire alarm control unit.

        _*Exceptions*_:
        1. Automatic sprinkler systems protecting one- and two-family
        dwellings.
        Doesn't apply to the buildings you've described

        2. Limited area systems serving fewer than 20 sprinklers.
        Doesn't apply to the buildings you've described

        3. Automatic sprinkler systems installed in accordance with
        NFPA 13R where a common supply main is used to supply both
        domestic water and the automatic sprinkler system, and a
        separate shutoff valve for the automatic sprinkler system is
        not provided.
        Depending on the underground supply, might or might not apply

        4. Jockey pump control valves that are sealed or locked in the
        open position.
        Doesn't apply to the PIV

        5. Control valves to commercial kitchen hoods, paint spray
        booths or dip tanks that are sealed or locked in the open
        position.
        Doesn't apply to the PIV

        6. Valves controlling the fuel supply to fire pump engines
        that are sealed or locked in the open position.
        Doesn't apply to the PIV

        7. Trim valves to pressure switches in dry, preaction and
        deluge sprinkler systems that are sealed or locked in the open
        position.
        Doesn't apply to the PIV

It does appear, based entirely on the information you've provided, that electrical supervision is required for the PIV.

And, not to split hairs or to be pedantic, California is not under the regulations in the 2013 IFC. California, as it does with almost everything, has made it's own modifications to that document and has issued the 2013 California Fire Code, which has as of January 1 been replaced with the 2016 edition of the CFC.

Chapter 80 of that document contains a list of the applicable editions of various standards and codes, including the NFPA documents. Further, that chapter of the CFC contains language on changes to the NFPA documents. As an example - in California, the reduction of the remote area size for use of quick response sprinklers in an area with a ceiling height of 20' or less is not allowed in ordinary hazard occupancies, even though NFPA 13 does allow that reduction.

I've had to deal with some terribly angry contractors who were unaware of those provisions. They've said some pretty creative and hostile things when I've pointed them out, including some I'm sure aren't true, as I have a photo of my parents' wedding, and it was 14 years before I was born!

sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***

On 01/23/2017 9:25 AM, Owen Evans wrote:

    As most of you know, I work exclusively with 13D systems. I do on
    occasion get questions on the big boy systems, 13 and 13R.  The
    property in question is a boutique hotel, two buildings. One
    building is a two story, fifty room hotel and the other building
    is two story, restaurant on the first floor and banquet facility
    on second floor with a roof deck. Each building has a FDC and a
    PIV. I am in California which is under the 2013 IFC.

    I recently had the question asked "does the PIV require electrical
    supervision?"  NFPA states a lock is adequate, the 2013 IFC states
    electrical supervision is required, with exceptions. I get
    different answers form different people. I'm thinking it's the
    more restrictive  2013 IFC. Which is it?

    Thank you,
    Owen Evans


    _______________________________________________
    Sprinklerforum mailing list
    [email protected]
    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected] <mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to