John, I agree with your 'common sense' statement, so this has been bothering me since you posted it.
I'm looking at NFPA 13 (2013), Fig. 8.6.5.2.2, and imagining my cubicle at the office. "A"=~36" and "B"=~30". The next sprinkler to the right is about 11' from the partition. My space is to the right side, and I have a kind of narrow counter against the partion with papers and prints scattered across it. Now I imagine the sprink shown in the fig activating, and 20-30% of the pattern being thrown over the partition and landing on the floor a few feet beyond the counter. Maybe The Committee felt that type of thing would be acceptable for LH but not OH? Brad On Jan 28, 2017 11:39 AM, "John Paulsen" <[email protected]> wrote: > Jeff: > > > > Amen on the “not clearly stated”! I saw that paragraph, but it appeared > to me to refer more to obstructions from the ceiling not the floor. I’m > trying to throw over the top of the partition and it would be nice if > NFPA-13 could give a spacing table for Ordinary Hazard like it does for > “Light Hazard only”. That’s the frustrating part, common sense says the > same or similar spacing would apply, but Ordinary Hazard is not included. > > > > Thanks, > > > > John Paulsen – SET > > Crown Fire System Design > > 6282 Seeds Rd. > > Grove City, OH 43123 > > P – 614-782-2438 <(614)%20782-2438> > > F – 614-782-2374 <(614)%20782-2374> > > C – 614-348-8206 <(614)%20348-8206> > > > > > > > > *From:* Sprinklerforum [mailto:[email protected]. > org] *On Behalf Of *Jeff Normand > *Sent:* Saturday, January 28, 2017 12:32 PM > *To:* [email protected] > *Subject:* Re: Floor mounted obstructions - ORDINARY HAZ > > > > Not that clearly stated but here's the NFPA 13 2016 edition > > > > > > 8.6.5.3.1 Continuous or noncontinuous obstructions that interrupt > > the water discharge in a horizontal plane more than > > 18 in. (450 mm) below the sprinkler deflector in a manner to > > limit the distribution from reaching the protected hazard > > shall comply with 8.6.5.3. > > > > 8.6.5.3.2 The requirements of 8.6.5.3 shall also apply to obstructions > > 18 in. (450 mm) or less below the sprinkler for light > > and ordinary hazard occupancies. > > > > A.8.6.5.3.3 When obstructions are located more than 18 in. > > (450 mm) below the sprinkler deflector, an adequate spray > > pattern develops and obstructions up to and including 4 ft > > (1.2 m) wide do not require additional protection underneath. > > Examples are ducts, decks, open grate flooring, catwalks, > > cutting tables, overhead doors, soffits, ceiling panels, > > and other similar obstructions. > > > > On Sat, Jan 28, 2017 at 11:10 AM, John Paulsen <[email protected]> wrote: > > I am trying to determine the proper deflector distance from a partition > with the top located 18” below the sprinkler deflector. This is an Ord Haz > Grp II Self Storage facility with standard spray QR Tyco TY-FRB TY3131 > uprights. Sec 8.6.5.2 doesn’t give a table like 8.6.5.2.2 which is for > Light Hazard only. > > > > If I have to space the heads as if the low partitions went all the way to > the deck, I will violate the 6’ minimum rule. What am I missing here? > > > > Thanks, > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org