Centered on the partial height partitions sounds perfect, and with a little
creative staggered spacing you could avoid baffles.

Odds are your AHJ would concur.

You're welcome and thank you for my weekend sprinkler puzzle ;)

Brad
On Jan 29, 2017 1:16 PM, <[email protected]> wrote:

> Thanks guys for your comments. I feel like I am trying to choose between
> evils here. If I can't place the sprinkler over the top of the low
> partition to spray on both sides, I am definitely going to cold shower on
> the 5' & 7' wide units....this project just became 4 stories of real
> problems.
>
> Thanks,
> John Paulsen
> Crown Fire System Design
>
> Get Outlook for Android <https://aka.ms/ghei36>
>
>
>
>
> On Sun, Jan 29, 2017 at 1:29 PM -0500, "Pete Schwab" <[email protected]>
> wrote:
>
> There have been submittals to SSI to allow the partition rule for OH. They
>> have been rejected since no one has submitted testing data. So in response
>> to the original question, yes you have to consider each partition as it
>> went to the ceiling and yes you still have to be concerned with cold
>> soldering. Many of the national self-storage facility owners/builders
>> understand that the top of storage must be 18” from the sprinkler deflector
>> (Usually accomplished with chicken wire) .
>>
>>
>>
>> Pete Schwab
>>
>>
>>
>> My opinion only and not that of the NFPA or any of its committees
>>
>>
>>
>> *From:* Sprinklerforum [mailto:sprinklerforum-
>> [email protected]] *On Behalf Of *Brad Casterline
>> *Sent:* Sunday, January 29, 2017 12:59 PM
>> *To:* [email protected]
>> *Subject:* RE: Floor mounted obstructions - ORDINARY HAZ
>>
>>
>>
>> John,
>>
>> I agree with your 'common sense' statement, so this has been bothering me
>> since you posted it.
>>
>> I'm looking at NFPA 13 (2013), Fig. 8.6.5.2.2, and imagining my cubicle
>> at the office. "A"=~36" and "B"=~30". The next sprinkler to the right is
>> about 11' from the partition.
>> My space is to the right side, and I have a kind of narrow counter
>> against the partion with papers and prints scattered across it.
>> Now I imagine the sprink shown in the fig activating, and 20-30% of the
>> pattern being thrown over the partition and landing on the floor a few feet
>> beyond the counter.
>> Maybe The Committee felt that type of thing would be acceptable for LH
>> but not OH?
>>
>> Brad
>>
>> On Jan 28, 2017 11:39 AM, "John Paulsen" <[email protected]> wrote:
>>
>> Jeff:
>>
>>
>>
>> Amen on the “not clearly stated”!  I saw that paragraph, but it appeared
>> to me to refer more to obstructions from the ceiling not the floor. I’m
>> trying to throw over the top of the partition and it would be nice if
>> NFPA-13 could give a spacing table for Ordinary Hazard like it does for
>> “Light Hazard only”. That’s the frustrating part, common sense says the
>> same or similar spacing would apply, but Ordinary Hazard is not included.
>>
>>
>>
>> Thanks,
>>
>>
>>
>> John Paulsen – SET
>>
>> Crown Fire System Design
>>
>> 6282 Seeds Rd.
>>
>> Grove City, OH 43123
>>
>> P – 614-782-2438 <(614)%20782-2438>
>>
>> F – 614-782-2374 <(614)%20782-2374>
>>
>> C – 614-348-8206 <(614)%20348-8206>
>>
>>
>>
>>
>>
>>
>>
>> *From:* Sprinklerforum [mailto:sprinklerforum-
>> [email protected]] *On Behalf Of *Jeff Normand
>> *Sent:* Saturday, January 28, 2017 12:32 PM
>> *To:* [email protected]
>> *Subject:* Re: Floor mounted obstructions - ORDINARY HAZ
>>
>>
>>
>> Not that clearly stated but here's the NFPA 13 2016 edition
>>
>>
>>
>>
>>
>> 8.6.5.3.1 Continuous or noncontinuous obstructions that interrupt
>>
>> the water discharge in a horizontal plane more than
>>
>> 18 in. (450 mm) below the sprinkler deflector in a manner to
>>
>> limit the distribution from reaching the protected hazard
>>
>> shall comply with 8.6.5.3.
>>
>>
>>
>> 8.6.5.3.2 The requirements of 8.6.5.3 shall also apply to obstructions
>>
>> 18 in. (450 mm) or less below the sprinkler for light
>>
>> and ordinary hazard occupancies.
>>
>>
>>
>> A.8.6.5.3.3 When obstructions are located more than 18 in.
>>
>> (450 mm) below the sprinkler deflector, an adequate spray
>>
>> pattern develops and obstructions up to and including 4 ft
>>
>> (1.2 m) wide do not require additional protection underneath.
>>
>> Examples are ducts, decks, open grate flooring, catwalks,
>>
>> cutting tables, overhead doors, soffits, ceiling panels,
>>
>> and other similar obstructions.
>>
>>
>>
>> On Sat, Jan 28, 2017 at 11:10 AM, John Paulsen <[email protected]> wrote:
>>
>> I am trying to determine the proper deflector distance from a partition
>> with the top located 18” below the sprinkler deflector. This is an Ord Haz
>> Grp II Self Storage facility with standard spray QR Tyco TY-FRB TY3131
>> uprights. Sec 8.6.5.2 doesn’t give a table like 8.6.5.2.2 which is for
>> Light Hazard only.
>>
>>
>>
>> If I have to space the heads as if the low partitions went all the way to
>> the deck, I will violate the 6’ minimum rule. What am I missing here?
>>
>>
>>
>> Thanks,
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>> org
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>> org
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to