I don't think there is a standard practice on these things. 

I've seen densities ranging from 0.2/1500, 0.2/3000 and 0.3/2000.

I only do these if there is an FPE that has specified the criteria. 



Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jan 30, 2017, at 12:51 PM, T. Silva <[email protected]> wrote:
> 
> Was OH2 specified or something you came up with? I was also looking at a self 
> storage facility with approx 11 feet height to bottom of joists and trying to 
> figure out the occupancy? What is the industry practice?
> 
> Tony  
> 
> From: "John Paulsen" <[email protected]>
> To: [email protected]
> Sent: Monday, January 30, 2017 8:06:08 AM
> Subject: RE: Floor mounted obstructions - ORDINARY HAZ 
> 
> Thanks Rocci,
>  
> I discussed the situation with the contractor this morning and spacing the 
> heads over the top of the partitions seems to be the only logical course to 
> take. I will recommend that they meet with the plan reviewer and AHJ to 
> discuss the design approach. We have done a few of these multi-story, self 
> storage facilties with similar wall arrangements and while I admit the threat 
> to life is relatively small for these facilities, it might be a good time for 
> full scale fire test to give us better design direction before too many more 
> are built. Especially when you consider the varying degrees of hazardous 
> commodities people tend to place in their units.
>  
> Everyone involved in the project is trying to provide the best protection 
> possible within the scope of the contract documents for this project. 
> Sometimes when you come across one of these grey areas, it’s hard to 
> determine a course of action that you are confident you can defend in the 
> event of a fire incident.
>  
> Thanks to all who have contributed to this question, your input has been 
> greatly appreciated!
>  
> In the immortal words of Captain Binghampton.. “Sometimes I could just 
> scream” (And yes I know I’m dating myself)
>  
> Thanks,
>  
> John Paulsen – SET
> Crown Fire System Design
> 6282 Seeds Rd.
> Grove City, OH 43123
> P – 614-782-2438
> F – 614-782-2374
> C – 614-348-8206
>  
>  
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Rocci Cetani 3
> Sent: Monday, January 30, 2017 9:38 AM
> To: [email protected]
> Subject: RE: Floor mounted obstructions - ORDINARY HAZ
>  
> I spoke with Matt Klaus about this at the AFSA convention and he basically 
> said there isn’t a “great answer” Try and place sprinklers over the tops of 
> the walls, if that’s not possible due to the size of the units have them, 
> build them higher, stagger the heads, and or get with the contractor and AHJ 
> and have them “approve” a method that has the most common sense….. My 
> response was that although the AHJ might be approving it ultimately  it’s the 
>  contractor that will be held liable in the event of a fire (and grilled by 
> the insurance attorneys), he agreed and said at least if you have something 
> in writing from the AHJ is shows the situation was discussed and this was the 
> best case scenario everyone could agree on….
>  
> Rocci Cetani III, CET
> Designer
> Water-Based Fire Protections Systems Layout, Nicet Level III
>  
> Northern California Fire Protection Services Inc.
> 16840 Joleen Way Bldg. A
> Morgan Hill, CA 93037
> P-(408) 776-1580 EXT.111
> F-(408) 776-1590
>  
>  
> [email protected]
> www.norcalfire.com
>  
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
> contain confidential information
> belonging to the sender. The information is intended only for the use of 
> individual or entity named above. If you are not the intended recipient, or 
> the employee or agent responsible to deliver this message to the intended 
> recipient, you are hereby notified that any disclosure, copying or taking of 
> any action in reliance on the contents of this information is strictly 
> prohibited. If you have received this transmission in error, please 
> immediately notify us by telephone to arrange for return of the documents.
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of John Paulsen
> Sent: Saturday, January 28, 2017 9:11 AM
> To: [email protected]
> Subject: Floor mounted obstructions - ORDINARY HAZ
>  
> I am trying to determine the proper deflector distance from a partition with 
> the top located 18” below the sprinkler deflector. This is an Ord Haz Grp II 
> Self Storage facility with standard spray QR Tyco TY-FRB TY3131 uprights. Sec 
> 8.6.5.2 doesn’t give a table like 8.6.5.2.2 which is for Light Hazard only.
>  
> If I have to space the heads as if the low partitions went all the way to the 
> deck, I will violate the 6’ minimum rule. What am I missing here?   
>  
> Thanks,
>  
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to