It's in the book.  It moved from 8.16.1.5 in the 2013 edition to 8.2.4 in the 
2016.   The section you want in the 2013 is 8.16.1.5.2.

However, in 2013 CA amendments, the OSFM made a numbering error and created an 
amendment to 8.16.1.5.1 and its subordinate sub-subsections that should have 
referenced a different set of numbers.  That's made the issue a bit more 
complicated than it should be but the bottom line is that the exception you're 
looking for is in the standard.

SML

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jerry Van Kolken
Sent: Monday, January 30, 2017 2:09 PM
To: [email protected]
Subject: When is a Floor control not required

In Late 2015 there was an ASFA Webinar about the changed to NFPA 13 (2016). 
During that webinar there was a brief discussion about floor controls, and not 
needing one for feeding a small area on another floor level (i.e. top of stairs 
on a roof level access). Is there code explaining this exception or is this 
more up to the AHJ?

Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730