A word of caution - a single building with multiple systems and multiple FDC's 
could be problematic for the responding Fire Department.  Which FDC should be 
charged in a fire event?

Pre-fire planning, signals from FACP, dispatch, FDC signage all come into play.

J. Scott Mitchell, PE
Senior Fire Protection Engineer
Mission Engineering
CNS Y-12 | 865-576-5258
CNS PTX | 806-477-5883


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, February 06, 2017 10:40 AM
To: [email protected]
Subject: RE: (1) FDC or (2)

I'd provide 2 separate FDCs, one attached to each riser if there is no issue 
with access.

If they were connected and one system was taken out of service due to some 
event (fire, explosion, weather related) and the piping system was compromised, 
the FDC would be useless for charging the other system.

I've seen warehouses where one system had been compromised, one by building 
collapse in a fire event, one where the building was hit by a microburst and a 
wall was taken out, which broke the fire main.  The other portions of the 
buildings affected were still operable since they were completely separated.

Let each system stand alone.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Monday, February 06, 2017 10:31 AM
To: 
[email protected]<mailto:[email protected]>
Subject: (1) FDC or (2) [EXTERNAL]

I'm working on a storage building that because of the way the building was 
built each "side" has its own Riser with its own FDC connection (picture a big 
horseshoe shape). The architect has requested that a single FDC be located on 
the corner of one of the building sides. Is it feasible to do this and tie the 
systems together via the FDC pipe or does each Riser still require its own FDC 
connection?

Brian Harris, CET