Brian, If FDC supply pipe were run from a single FDC to both system risers,
and connected to the system risers between the BFP (or other supply check
valve) and a system control valve, either of the systems could be shut down
for maintenance/repair without impairing the FDC for the in-service system.
Each system riser would need its own FDC check valve.  Doing this might
require more bulk pipe and a couple more control valves.

 

Ed Kramer

Bamford Fire

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brian Harris
Sent: Monday, February 06, 2017 9:31 AM
To: [email protected]
Subject: (1) FDC or (2)

 

I'm working on a storage building that because of the way the building was
built each "side" has its own Riser with its own FDC connection (picture a
big horseshoe shape). The architect has requested that a single FDC be
located on the corner of one of the building sides. Is it feasible to do
this and tie the systems together via the FDC pipe or does each Riser still
require its own FDC connection?

 

Brian Harris, CET

BVS Systems Inc.

Design Manager