Brian, If FDC supply pipe were run from a single FDC to both system risers, and connected to the system risers between the BFP (or other supply check valve) and a system control valve, either of the systems could be shut down for maintenance/repair without impairing the FDC for the in-service system. Each system riser would need its own FDC check valve. Doing this might require more bulk pipe and a couple more control valves.
Ed Kramer Bamford Fire From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Monday, February 06, 2017 9:31 AM To: [email protected] Subject: (1) FDC or (2) I'm working on a storage building that because of the way the building was built each "side" has its own Riser with its own FDC connection (picture a big horseshoe shape). The architect has requested that a single FDC be located on the corner of one of the building sides. Is it feasible to do this and tie the systems together via the FDC pipe or does each Riser still require its own FDC connection? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com <http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935