As per NFPA 14, in a combined standpipe/sprinkler system, the minimum pressure 
at the outlet of most remote 1 1⁄2 in. hose station should be 65psi. As 
standpipe and sprinkler riser in shared, I want to reduce the pressure to the 
sprinklers to around 15psi in order to reduce the total sprinklers flow demand 
and finally to select a smaller fire pump. 

What is the most cost-effective way to do that? Can I use a restrictor? For 
example, if the main sprinkler pipe at each floor is 3", can I install a short 
1" pipe just at the beginning to reduce sprinklers pressure. Can I do that? I 
checked this in a hydraulic calculation software and in works fine, but I am 
not sure if this is a right way.