Steve,

Thanks for your reply and your kind trying to understand me. I know it’s 
difficult for you to state what is not complied to NFPA. 

Tehran Fire Department, as the only AHJ, allows 3500GAL in light hazard 
occupancies and if QR sprinklers are used, they allow 2500GAL water tank. As 
the buildings are not connected to city main, they have difficult time 
providing the space for big water tanks. When it comes to water tank size, as 
NFPA is requesting too much, they try to somehow comply to European codes.

Check EN12845 which is used in Europe, page 47, requesting 11 cubic meter 
(2900GAL) water tank for light hazard occupancies.

http://sarian.ir/EN12845.pdf

Maybe, the “Risk Acceptance Level”, infrastructure and local economy play an 
important role in their decision and maybe just ignorance!. We all know that 
most of the fires in light hazard occupancies like residential and office 
buildings are extinguished with less than 3 activated sprinklers. So maybe they 
calculate the system based on 3 operated sprinklers and they accept the risk. 
VdS standard in Germany is also considering 4 activated sprinklers.  Most 
European cities are also not connected to city main water.

http://sarian.ir/VdSCEA4001en.pdf

Considering all mentioned differences between how Americans vs. Europeans think 
about sprinkler design, I am thinking to find a solution to somehow cover some 
of the weaknesses in our design here in Iran.


Best,
Reza
www.sarian.ir <http://www.sarian.ir/> 

 

 

Reza:

I understand your earnest interest in finding a solution, but what you’ve done 
is pose questions to the Forum and not fully informed of all conditions, which 
compromises us who may answer.  For example, the idea that you’re “limited” to 
a 3,500 gallon water tank is an arbitrary figure and simply ridiculous.  Who is 
limiting this?  If you’ve been told to proceed with system design and not been 
given the resources to design or install a tank of adequate capacity, then that 
is a DEFICIENCY and outside the scope of the NFPA standards.   

 

So the first correspondence should be a letter to whoever is specifying or 
“limiting” the tank capacity to inform them that it needs to be the appropriate 
capacity.   And I’m failing to grasp what a restrictor gets you in any case.  
If the hazard group is Light, your duration requirement (with electronic 
monitoring of your system) is 30 minutes; for Ordinary it’s 60 minutes.  Using 
your theoretical demand with restrictor of 314 GPM + 100 PSI hose allowance, 
you have to prove 414 GPM for 30 or 60 minutes, no?   So you need a tank with 
12,420 or 24,840 usable gallons capacity.   Nominal reduction of the sprinkler 
demand isn’t and adequate solution.  

 

It seems to me that with a deficiency of such extraordinary magnitude you want 
the first two or three sprinklers to work as well and reliably as possible, 
which means forget the restrictor.   I’ll leave it to you to determine who to 
resolve your water supply duration problem, but if this was in the USA it would 
be a non-starter.    

 

My opinion only,

SML

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Reza Esmaeili
Sent: Thursday, February 09, 2017 8:57 AM
To: [email protected]
Subject: RE: Reducing Sprinklers' Pressure in a Combined Standpipe/Sprinkler 
System

 

Thanks for your replies David and Art. 

To Steve: Installing a restrictor to lessen the flow at sprinklers is not just 
for reducing pump size to save a few Dollars. It’s also about the water tank 
size. Our buildings are not connected to the city main like yours and we have 
to rely on a small water tank size around 3500GAL. If I don’t reduce the 
sprinkler system flow, the water tank is finished in less than 7 minutes.

To Art: At first I was also thinking of reducing the size of main pipe to the 
sprinklers to hydraulically reduce pressure/flow (instead of installing a 
restrictor just at the beginning). But it seems in this way, the pressure drop 
is very vulnerable and very related at where the sprinklers are going to be 
activated. Imagine I reduce 3” to 2” and the main pipe lenght to the most 
remote sprinkler is 120ft.

- If 12 most remote sprinklers are activated (120ft from the riser), the 
pressure behind the sprinklers is around 20psi, so the total flow is around 
320GPM.

- If 12 sprinklers in the middle are activated (60ft from the riser), the 
pressure behind them is around 40psi, so the total flow is around 420GPM.

I want to say when you are going to reduce the pressure in a pipe length, you 
are not sure when the sprinklers are going to operate. At the end of pipe, in 
the middle or at the first? So you are not sure how much the pressure if going 
to drop. But if you are installing a reducer just at the beginning, you 
suddenly drop the pressure and no matter where there sprinklers are going to 
operate.

Best,

Reza

www.sarian.ir <http://www.sarian.ir/> 

 

I suggest you reduce pipe size on the main run to increase pressure and reduce 
the flow hydraulically.

You should be able to balance flow and pressure with the proper pipe sizes.

 

Art Tiroly

ATCO Fire Protection.

 

From: Sprinklerforum [mailto:[email protected] 
<https://mg.mail.yahoo.com/neo/b/[email protected]>
 ] On Behalf Of Reza Esmaeili
Sent: Thursday, February 09, 2017 10:50 AM
To: [email protected] 
<https://mg.mail.yahoo.com/neo/b/[email protected]>
 
Subject: RE: Reducing Sprinklers' Pressure in a Combined Standpipe/Sprinkler 
System

 

Thanks for your reply Steve.

 

*       The local code requires 100gpm@65psi 
<https://mg.mail.yahoo.com/neo/b/compose?to=100gpm@65psi>  for the 
hydraulically most remote hose connection which are class II 1 1⁄2 in hose 
stations. Both hose stations and sprinklers are connected to a single wet pipe 
riser. The pumps should be selected based on sprinklers demand + standpipe 
demand. The local code ask to simply add 100 gpm to sprinkler demand. For 
example, if sprinkler demand is 400gpm, just add 100 gpm for standpipe. These 1 
1⁄2 in hose stations are not for occupant use and not small hose connections as 
stated in NFPA 13. Fire fighters in my country use 1 1⁄2 connections, not 2 1⁄2.

 

*       The city water main is not able to supply the demand, so a private 
water tank, located in the basement is supplying both the sprinklers and 
standpipe.

 

*       Travis also suggested using 4.2k sprinklers which is a good idea, but 
there are some problems. First the water is not clean for such a small orifice. 
Second 4.2k is not available in our market!

 

*       As each sprinkler is covering 130 sq.ft, and the required density is 
0.15, so the minimum required flow for each 5.6K sprinkler is 19.5GPM. That is 
to say 13psi is the minimum pressure at the most remote sprinkler.  After 
installing the restrictor, the minimum pressure is 21psi which is ok.

Coming back to the original question:

 

Am I allowed to install a restrictor? For example, if the main sprinkler pipe 
at each floor is 3", can I install a short 1" pipe just at the beginning to 
reduce sprinklers pressure? This 0.5m length, 1" pipe can suddenly drop the 
pressure from 65psi to 30psi. Then the most remote sprinkler pressure at the 
top floor would be around 20psi which I like. If required, the more I get 
nearer to the pump located at the basement, I have higher pressure, and I can 
cut more pressure using this small pipe. For example if the pressure behind the 
hose station at the ground floor is 110psi, I can use a 2m length, 1" pipe just 
at the beginning of the pipe supplying the sprinklers to drop the pressure from 
110psi to 20psi. Do you see any problems?


Best,
Reza
www.sarian.ir <http://www.sarian.ir/> 

 

From: Reza Esmaeili [mailto:[email protected] 
<https://mg.mail.yahoo.com/neo/b/[email protected]> ] 
Sent: Thursday, February 9, 2017 6:29 PM
To: '[email protected]'
Subject: RE: Reducing Sprinklers' Pressure in a Combined Standpipe/Sprinkler 
System

 

Hi Craig, Travis, Scot and Tim,
Thanks for your replies. I am using Pipenet Spray/Sprinkler software which is 
mainly a hydraulic colocation software not used in the US. 

You are right Craig, when less sprinklers are activated, the restrictor can't 
lessen the pressure, but in this case I have low flow because of less opened 
sprinklers. Look at the below scenarios. The first scenario is without 
restrictor and the second and third are with restrictor. If I don't install a 
restrictor, my sprinkler system demand is 451gpm. But if I install a 
restrictor, my maximum sprinkler system demand is 314gpm.


1-    First scenario: No restrictors, 12 sprinklers activated at the most 
remote area at the top floor:
-    The pressure at the beginning of sprinkler piping: 65psi
-    The pressure just behind the most remote sprinkler: 45psi
-    Total flow for all 12 open sprinklers: 451gpm

2-    Second scenario: 0.5m length, 1” pipe, 12 sprinklers activated at the 
most remote area at the top floor:
-    The pressure at the beginning of sprinkler piping: 65psi
-    The pressure after restrictor: 31psi
-    The pressure just behind the most remote sprinkler: 21psi
-    Total flow for all 12 open sprinklers: 314gpm

3-    Second scenario: 0.5m length, 1” pipe, 3 sprinklers activated at the most 
remote area at the top floor:
-    The pressure at the beginning of sprinkler piping: 67psi
-    The pressure after restrictor: 61psi
-    The pressure just behind the most remote sprinkler: 56psi
-    Total flow for all 3 open sprinklers: 127gpm

Best,
Reza

Cel: +98 9122444875
www.sarian.ir <http://www.sarian.ir/> 

 

Here’s a question, are you going to try to reduce the sprinkler system pressure 
to lessen the flow based on one sprinkler or two or ten flowing?  If you base 
it on ten but only have three flowing, your pressure reduction does not work 
the same.  

 The sprinkler demand we calc to prove is a product of required pressure and 
K-factor not provided pressure and K-factor.  Your calcs are to prove the 
system works based on the supply pressure and flow.  Every sprinkler system 
design will typically flow more than what is calculated since we are only 
proving the supply can meet the minimum design requirements. 

 We calculate a 1500 sq. ft. area and find a required flow and pressure to 
accomplish that.  But when only one or two sprinklers flow and the supply flow 
and pressure to that system are the same as when we calculated 10 or 12 
sprinklers, the discharge from a few will always be more than what is needed.

 Also, actual flow, even for the entire remote area will be more than the 
minimum calculated if there was any cushion in your calcs.  

 What calculation software are you using?  

 Basically, calculate what is required for the sprinklers, then calculate the 
standpipe and do not worry about the overage on the sprinkelrs.

 
Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] 
<https://mg.mail.yahoo.com/neo/b/[email protected]> 

 

From: Sprinklerforum [mailto:[email protected] 
<https://mg.mail.yahoo.com/neo/b/[email protected]>
 ] On Behalf Of Reza Esmaeili
Sent: Thursday, February 09, 2017 7:05 AM
To: [email protected] 
<https://mg.mail.yahoo.com/neo/b/[email protected]>
 
Subject: Reducing Sprinklers' Pressure in a Combined Standpipe/Sprinkler System 
[EXTERNAL]

 

Hi forumites,

As per NFPA 14, in a combined standpipe/sprinkler system, the minimum pressure 
at the outlet of most remote 1 1⁄2 in. hose station should be 65psi. As 
standpipe and sprinkler riser in shared, I want to reduce the pressure to the 
sprinklers to around 15psi in order to reduce the total sprinklers flow demand 
and finally to select a smaller fire pump. 

What is the most cost-effective way to do that? Can I use a restrictor? For 
example, if the main sprinkler pipe at each floor is 3", can I install a short 
1" pipe just at the beginning to reduce sprinklers pressure. Can I do that? I 
checked this in a hydraulic calculation software and in works fine, but I am 
not sure if this is a right way.

Best,
Reza