If CA follows NFPA 70 without any kinds of modifications or amendments, there is no restriction on the routing of a sprinkler line through an electrical room as long as you are outside the Working Space and the Dedicated Electrical Space as defined with NFPA 70, 110.26. The sprinkler line does not have to serve only the electrical room as some believe. See 110.26 (E) (1) (c).
One thing to note about electrical rooms is that if the electrical gear is oil filled, it's not going to be an ordinary hazard occupancy any more, sidewall goes away as an option. Be sure you know if the electrical gear is dry or oil filled. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 [email protected] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Tuesday, February 28, 2017 3:12 PM To: [email protected] Subject: Sprinkler in Electrical Rooms (in CA) [EXTERNAL] We've had resent jobs where the GC has told us to remove the piping from the electrical room and just install a sidewall. We've been following NEC 110.26 (f) (2008). Has there been a change to the electrical code / CBC requiring this? Jerry Van Kolken Millennium Fire Protection Corp. 2950 San Luis Rey Rd. Oceanside, CA 92058 (760) 722-2722 FX 722-2730