If CA follows NFPA 70 without any kinds of modifications or amendments, there 
is no restriction on the routing of a sprinkler line through an electrical room 
as long as you are outside the Working Space and the Dedicated Electrical Space 
as defined with NFPA 70, 110.26.  The sprinkler line does not have to serve 
only the electrical room as some believe.  See 110.26 (E) (1) (c).

One thing to note about electrical rooms is that if the electrical gear is oil 
filled, it's not going to be an ordinary hazard occupancy any more, sidewall 
goes away as an option.  Be sure you know if the electrical gear is dry or oil 
filled.